Differential Setting for Indirect DHW
![troutdog](https://secure.gravatar.com/avatar/43f09451f1bbe8374150f6b21378b858/?default=https%3A%2F%2Fvanillicon.com%2F6dba2bec7a43daef3d155df8eb68a009_200.png&rating=g&size=200)
I have a new Lochinvar KHB 199 Condensing Boiler with a SIT80 indirect tank. The factory differential setting is 6 degrees, which seems low. The installer has left all settings unchanged. (The boiler sends 170 degrees to the tank and tank temp set to 140).
Should I leave the 6 degree differential or do you recommend going to a larger number? My thought is to have a few less cycles.
Thanks.
Comments
-
the aquastat that come with some tanks are typically 15.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
If there's a .5° standby heat loss per hour, then big whoop. Twice a day to recover wont break you. If there's a big demand, you'll like that tight differential.
With the tank set to 140°, I'm sure there's a mixing valve tempering down to 120°, right? So going to a 10° diff should be fine in this case as long as everything is piped and sized correctly.
0 -
Just a small thank you to all in this post. I had the same question and got an answer here! FYI, my HTP ELU85WBN default dhw differential temp setting was zero!0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 100 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 101 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 934 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements