Steam pipe pitch
I don't think my steam pipe going back to my boiler is pitched enough to return water back to the boiler causing my water hammer in my steam baseboard. The is a chain used for a hanger that may have come loose. If I pull up on the chain will it give enough pitch? Pics included….
Comments
-
Return piping should drop 1" every 20 ft. Steam piping shoud drop 1" for every 40 ft.
That chain is fine for hanging light fixtures, not for steel pipe. I recommend you replace it and all those perf straps with real pipe hangers. This is called a clevis hanger. There are several other types, but perf strap isn't acceptable for schedule 40 pipe.
For 2" schedule 40 pipe, you should have a hanger every ten feet or less, every seven feet for 1" pipe, and the hanger rod should be at least ⅜". Make sure the mounts are secure and note the use of locking nuts.
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-241 -
thank you. Will these hangers work?
0 -
Yes. That's a clevis hanger. You'll also need some ⅜" threaded rod—enough to reach from the joists to the pipe in each location—some ⅜" nuts and as many rod hangers as you have pipe hangers. These search results should show the various kinds that are available.
I use the cast iron ones, but if you use the L brackets, use a nut above and below the bracket. You'll also need some screws to secure the rod hangers. I use 2" deck screws.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Just to be clear, these are the types I use, depending on whether I'm hanging it from the bottom or the side of the joist:
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements