Riello issue

dm1075k
dm1075k Member Posts: 4

I have a Riello 40 F5 that has not given my any trouble in 20 years. I have stayed on the maintenance regularly. A few weeks back it shut down and on refiring it would just hum. By turning the fan by hand, which had more resistance than it should, it " loosened up" and fired without issue for a day or two and then had the same problem. The Tech came and said it was the motor, which he changed but had the same issue a week later. He came back and replaced the oil pump, and has run for a week with no problems and now I am back to the same issue. When I want heat I turn the fan by hand to "loosen it" then it will fire no problem for a few cycles the will bind and not fire till I turn it by hand. Not sure what is going on here. It's a two pipe system if that makes any difference. At this point I probably will get a new burner after this season is over. Love to hear some more educated thoughts on this then I have at the moment. Thanks in advance

Comments

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505

    Tell your tech to keep changing parts…almost got them all.
    Was incoming voltage checked and confirmed?
    Wiring connections OK?
    Capacitor checked?
    Key between motor/pump good, installed correctly?

    There was an error rendering this rich post.

    HVACNUTSuperTech
  • dm1075k
    dm1075k Member Posts: 4

    yes, juice is all good, do not know about the capacitor but would I still get difficulty turning the shaft from the fan with electric off? How would the capacitor effect that with electric off? You make a great point about the key between pump and motor, that I will take a look at…..thanks Steve for the quick response!

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,157

    I have a Riello 40 F5 that has not given my any trouble in 20 years. I have stayed on the maintenance regularly. A few weeks back it shut down and on refiring it would just hum. 

    The reason the burner just Hummms… is because it forgot the words. Put the sheet music in front of the burner and see if the Hummm stops

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Solid_Fuel_Man
  • Big Ed_4
    Big Ed_4 Member Posts: 2,980

    You freed up the pump , if the oil supply is clean . I would replace the pump .

    20 years you had a good run . I would recommend, replace the Riello and get another 20.

    There was an error rendering this rich post.

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,157

    But really, The Pump is new and the Motor is new. You felt some resistance when you moved the fan by hand then the resistance was gone. What is the chance that there is something inside the fan or the fan housing that is causing the fan to stick. Did he clean the fan blades, and the fan housing?

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Steamhead
    Steamhead Member Posts: 17,326

    Is there a fiilter in the oil line before the burner? Has it been changed recently? Has water gotten into the tank?

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • HVACNUT
    HVACNUT Member Posts: 6,238

    So what was the reading on the cap? It should be 12.5 uF. +- 6%.

    I don't think the "spin by hand" test is reliable because you can't use your hand.

    There's very little play in the fan housing so if the fan wasn't aligned properly, you'd hear it rubbing.

    It's pretty hard to not put it together correctly. The drive key could be damaged but you'd think that would've been noticed during the motor replacement, then the pump replacement. BTW, was the pump pressure adjusted for your boiler and firing rate. It almost certainly isn't set out of the box. Was a combustion test done because the firing rate has changed?

    Was the bypass plug installed on the new pump?

    STEVEusaPASuperTech
  • dm1075k
    dm1075k Member Posts: 4

    thanks for everyone's input. Going to massage the burner to get me through the heating season( few more weeks here on Long Island). Then tear it down to see what's going on. If I can find same burner new, I will buy it and use the old one for parts. Thanks again.

  • SuperTech
    SuperTech Member Posts: 2,382

    Before you waste time and money on a burner I would try a replacement capacitor. It's standard practice to always replace a capacitor when replacing a PSC motor. The description of your problem sounds like what happens when a capacitor fails or doesn't have enough capacitance to start the motor.

  • Big Ed_4
    Big Ed_4 Member Posts: 2,980

    Either your oil supply is sucking up sand or you have a bad return line .

    Two pumps , grit and teflon tape can jam the pump gears . When they jam the pump lock up the motor . If the return line is blocked the pump will also lock up , if the seal holds out ..

    Either way ,I would Run an new single supply line to the tank if possable and instal a filtered tigerloop .

    There was an error rendering this rich post.

  • dm1075k
    dm1075k Member Posts: 4

    thanks big Ed and super tech, will take a look at both!

  • armstrongfarm
    armstrongfarm Member Posts: 1

    hey. So what was the problem?? I have exactly the same issue with my reillo 40 f5. I thought it was a bad motor. Always tripped but if i spun with a screwdriver as i push reset button it would fire up. So i changed motor. Week later same issue. Filters clean new pump screen. New nozzle. Orderd a capicitator. Just waiting on part to come

    In.

  • RTW
    RTW Member Posts: 104

    Dear Poster

    I have an older Reillo to. For what you paid for service and replacement of the motor and pump etc, you could have had a brand-new Reillo burner, but that's water under the bridge. Thus, post your repair & parts cost to date to compare to a new burner - just sayin

    Regards,

    RTW

  • apodias
    apodias Member Posts: 1

    A friend of mine has a riello 40 and it stopped working, and the fan was kind of tight so I loosened it by hand and it worked for a day and then it went out, so I changed the capacitor and it did the same thing. So then I hooked up both capacitors and now it works fine

    HVACNUTSuperTech
  • RTW
    RTW Member Posts: 104

    apodias " may be on to the real issue/cause of failure. I would add, the expensive parts replaced in OP post were clearly NEVER the problem - good luck getting a refund

    Regards,

    RTW

  • RTW
    RTW Member Posts: 104

    This may belong under a separate heading, but I see tech service as those that simply replace parts as a likely solution vs. actual understanding on how to fix the problem. I today, consulted a guy that repairs older appliances as to an issue with my circa 1964 Maytag washer that suddenly was not draining the water in tub ( I use it just for work cloths and have another washer for everything else). I figured it must be the "pump" needed replacement. On the contrary, was his response: "when did you last replace the belts that drive both the pump & tub". Well "never" I said and have owned it since 1996. Guess what, he had the new belt parts on a shelf in his shop . Thus, not the more expensive pump - if even still available

    Regards,

    RTW