Hydronic system
Hi I installed a new gas hydronic system 133,000btu.system is building up pressure.I drain system to 12lb bled the 2 zones.2 days later same thing turned off feeder to system check ok. replaced feeder and went to a 60lb expansion tank. Next day same condition system building up pressure and go off on relief valve. Any suggestions?
Comments
-
Is there a tankless coil or insirect hot water tank that may have a pinhole leak?
Are you certain the feedwater vavle is working one hundred percent (if soldered was it possibly overheated)?
Any chance you took care of the problem but the gauge is inaccurate?
Any chance you took care of the problem but the relief valve has blown off so many times that it no longer pops at 30 psi and is now relieving at say 20 psi?
0 -
After several new parts I had system operating and it build up to 20lbs.It's seems to build up at night . I even turned off feeder and system was at 20lbs and then went to 25 lbs with the feeder off. The relief valve is operating normally..
0 -
Any chance the new expanstion tank was not pre-charged to 12psi? Is it a bladder type (Extrol 60 for example)?
0 -
Yes I also checked that.. And I was advised that was the same problem with the old boiler toomuch pressure..and the 3 parts where replace relief,tank and feeder.
0 -
Is there a tankless coil or indirect hot water tank?
Are you certain the feedwater valve actually stops flow of water to the boiler?
In other words is there any possiblilty there is another source of water being introduced to the boiler?
Please post a few photos, sometimes a photo helps everyone learn.
0 -
The water feeder was installed above the circlater pump and 3 speed pump any chance that's pulling water from feeder. There's no coil or storage tank. Looked around house and crawl space no other water feed to system.
0 -
I tried to look closeuly at your phots and was trying to play detective.
Ideally the pump would not be on the return but on the supply - after the expansion tank/separator. But I'm not convinced this is your problem.
I notice the Nibco valve on the right side of your photo that I assume is the feedwater valve (near the zone valve marked "2". This particular valve has a drip of solder on the bottom of the valve body. Is there any chance this valve was overheated when it was installed and is not shutting off the flow completely?
I did not see a pressure reducing valve, where is it?
You mentioned a 60lb expansion tank. Not sure what you meant by that, but the tank in your photos is an Extrol 30 that should have a factory charge of 12psi.
0 -
The feeder is at top and I didn't take any photos of the new 60lb expansion tank. would a small water leak in system expand and have a leak when hot and close when cooled contribute to problem?
0 -
you need to explain what a "60lb expansion tank" is. hopefully that is not what you have the pressure in the tank set at.
0 -
i changed the 30lb tank to a 60 lb expansion tank which was set at 12lbs.I was running out of ideas to eliminate the pressure problem. I installed a 60lb tank .which didn't help. This is a mystery of the increasing pressure that I'm out of solutions.. Maybe something I've over looked
0 -
I think you mean you changed out a number 30 extrol expansion tank, with a number 60 extrol expansion tank. 30lb and 60lb mean something different.
Can you send a couple more pics of the water feeder, as it is installed and how it ties into the hydronic system. Currently in the pictures it looks like it is still open to the boiler system, if it is not working correctly it could be over pressurizing your system
0 -
Yes a #30 fora#60 tank..I don't have more pictures but the water feeder is piped into the return above the pump.
0 -
We see your situation often here and I don't think we've ever arrived at a solution. Scott mentioned that the pump is in the wrong location - should be pumping away from the x-tank.
How long has this system been up and running? Have you spoken to the installer about the problem?
I've noticed that Spirotherm air separators can block the connection of the x-tank to the system. I would remove the x-tank and see if there's any debris at the bottom of the Spirotherm unit. I would even go so far as to remove the top of the Spirotherm to check for any blockages. Maybe you can even do that before you remove the x-tank.
Too bad that gas pipe goes right in front of where you want to work. Kind of gets in the way.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab2 -
That was all checked the removal of the c tank and spiro vent disconnected to check internal all checked out good. This problem was with the old system also. Unit eas installed Nov 2022.. the old boiler was installed back in the 80's
-1 -
-
every time the circ kicks on it drops pressure at the inlet, could be 4, 5 psi or more. That could cause the fill valve to kick on and add more pressure, so you end above the static fill pressure when the circ shuts off
I'd move the Expansiontank to this 1/2" copper fill line
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream3 -
I'll try relocating the x tank..Thank for all for the help greatly appreciated .
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements