Fixing a Small Leak on a Big Manifold
4" black pipe, malleable iron tees, brass shutoff valves
All joints taped (Blue Monster) and doped (Megaloc).
After several months of operation we noticed tiny drips at two of the joints, a malleable tee and a brass ball valve. (The thousand or so other joints throughout the system are holding up fine.)
What to do?
- Drain water, disconnect boilers, cut pipe, disassemble, thread cut ends, add a union, reassemble?
- Drain water, solder joints? Will solder work on a threaded fitting that is already taped and doped?
- Hydronic Leak Sealant such as PurePro or Hercules Base Hit II?
- Epoxy putty applied to outside of pipe? Pro Poxy20 or JB Weld?
Luke
Comments
-
-
-
-
-
Take apart and redo. Consider pre-made connectors with male ends that often come with unions. Something like these https://www.supplyhouse.com/Chamflex-CH125012FM1000-1-1-4-x-12-ChamFlex-Hose-Swivel-MNPT-X-Fixed-MNPT
My biggest concern is why are (only) these joints leaking?1 -
Are these tiny leaks? If so, I’d tear long strips of cotton cloth and wrap those joints. Watch them and see if they stop leaking over time. If it’s low pressure and tiny leaks they might scale and seal up. If they don’t I’d take everything apart and redo it. That’ll be a tough job with 4” pipe so I’d try the cotton wrap first.1
-
-
👍ball wick if you can go round and round where the threads meet the fitting and valve.0
-
Take it apart and fix it right. Use a little dope (sparingly) on the inside threads of the fitting. Tape and dope on the male portion some of which gets "pushed out" of the joint so doping the inside helps.
In fact, read the instructions on a can of Rectorseal True Blue. The recommend doping the inside threads on anything over 1 1/4"3 -
I'm confused about what you are proposing Scott. Are you saying use a 4" diameter flex hose instead of a union? I've used a similar product from HoldRite for connections to the individual boilers, to the buffer tank, to the indirect, etc. but HoldRite only makes them up to 2" diameter.ScottSecor said:Take apart and redo. Consider pre-made connectors with male ends that often come with unions. Something like these https://www.supplyhouse.com/Chamflex-CH125012FM1000-1-1-4-x-12-ChamFlex-Hose-Swivel-MNPT-X-Fixed-MNPT
My biggest concern is why are (only) these joints leaking?Luke Stodola0 -
Yup, we doped the female threads on initial assembly. Its possible I was just a little too gentle on the tightening. I didn't want to damage the brass valve by going too tight.EBEBRATT-Ed said:Take it apart and fix it right. Use a little dope (sparingly) on the inside threads of the fitting. Tape and dope on the male portion some of which gets "pushed out" of the joint so doping the inside helps.
In fact, read the instructions on a can of Rectorseal True Blue. The recommend doping the inside threads on anything over 1 1/4"
We used a 4' pipe wrench, with some EMT over the handle as cheater bar, so I thought it was tight enough. But we can always get one more person on the cheater bar to make it another turn.
Between the two drips its probably less than 1 oz of water per day. Didn't even notice it till we were putting the insulation on.Luke Stodola0 -
The issue with hydronic leaks is the expansion and contraction as it heats up and cools down, so it would be a reach to think it will seal itself off. Often the leak gets worse as the hot, cold swing continues.
It’s a gamble, but if you are installing insulation it should be leak free, or you will be replacing expensive insulation also.
Bummer, but I suspect you know the right way to fix it😏Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream3 -
@lkstdl I assumed your leaks were on the individual boiler pipe, not the actual 4" common header. They also make four inch "pump connectors" that might help you out. We often have welded headers made up when we're using 4" and larger pipe.
0 -
-
-
Mega press would also work. You could rent the tool and jaws if you don't own them
0 -
-
-
-
-
Y,This is a new job under warranty,, your name is on it.. as Hot Rod said,, epoxy is for something old you don't want to touch or open a can of worms...and...for amateurs...Bite the bullet and take apart.. if you used enough isolation valves,, its easy. Ok, In this application, larger screw pipe, I ALWAYS use LAMPWICK (Thinner cotton string AKA "Spool" wick) NOT BALLWICK (Same material but fatter and used on waste lines as a homemade washer). ALSO, Go around 6 - 8 times IN THE THREAD roots (grooves), apply Permatex, GRRRIP, or one of The Heavy, glue, Rectorseals...the ones with a heavy petroleum odor. Apply liberally To wicked threads and really work it in. Also, really work it in to the female threads too. (Shhhh...Most codes prohibit this), but wipe any excess dope to limit the dope in the system's media.
Screw it together very tight but don't split the fittings! Wipe off all excess dope let it run a few days, and if there is any weepage, the Quick Wick should absorb it and swell. If it still weeps, Neck-crank it tighter. I LOVE Blue Monster tape on waste lines and some other applications, but my tried and true method for screw pipe of all sizes is Quick Wick and Megaloc or good teflon Paste like Real-Tuff or Rectorseal White. A questionable thread or something I have to take apart is getting the Permatex, et al. I was taught this 40 years ago from Deadman Who had 50 years in who were taught by their Deadman and so on and so in..back to the early days of Mr Whitworth and his invention. I for one REVERE these men before me...they were much 🤓 Smarter and erudite than some of you'll give them credit for. They INVENTED and DEVELOPED what you want to tinker with, CRITIQUE, and play Doubting Thomas with. Their hard work and ingenuity have stood the test of time, safely heating homes all over the world. Mr Watts, Gil Carson, And What Dan Holohan has brought us in education at the knee of these great men..is PRICELESS...Take it ti the Bank!! .. My Mount Rushmore Of Heating Heroes. Last, they did this all sans power tools, even electricity, computer, youtube, labor laws about much more than an 8 hour day. I'm all for cutting edge, new technology and I embrace the good, proven stuff, but what I have seen is that The Deadman WERE AND ARE right about most things we install every day. Sorry, I'm not dismissing their PROVEN track record... Mad Dog
0 -
-
Sealants are gimmicks and at best stop gap. Would never put that in New boilers. As long as you as yiu have service valves, and don't have to bleed radiators in 100 apartments, just bite the bullet and fix the leak. We've all been there. Nad Dog
1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements