Jamie, I started with CT87K0
-
OK, were all tired of this trivial problem, think we beat it to death, I want to thank everyone for your patience and input. To answer the question the load of the zone valve does go through the thermostat it is not isolated at the control board. Also system low voltage is 26V and when loaded down with both zones calling it goes to 22.5V. I am going to keep the Honeywell CT87K on line in the 2nd floor and monitor it. New LUX stat arrived today, but I want to see if the yo-yo acts up. For sure, stay away from the Mechanical Honeywell in these applications.
Thanks to all, I'm sure you have plenty more post to address on this site.
Matt
0 -
@hot_rod In the TACO 3 zone controller (ZVC403) I don't think there are any zone relays like in the 120 Volt units. So the thermostat sees the Zone Valve loads in this case.hot_rod said:Doesn't the thermostat just see the relay in the Taco box, not the actual zone valve load? I thought the relay isolated the load from the stat?
This sure sounds like more than a T-stat issue.
@Camperch, I believe the intended current path is what I marked in Red, any other path near the magnet may just be coincidental by the design. I believe the current does not go through the bi-metal (curly-Q) that senses the temperature. Depending on the setting it does go through the resistance wire (probably an alloy and not bi-metal) for the Heat anticipator. Glad you have it all working better now.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System1 -
109A_5 -----Yes, I agree, thanks0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements