Cold fire boiler and idwh
AdamS
Member Posts: 2
Ibc hc33-160 and IDHW IBT 40, Taco SR506-6 relay. Here’s my problem.
The installer used a Taco SR 506-6 zone relay. We keep running out of hot water and I discovered why.
I noticed when I looked at the control board there’s no wires in the aqua stat low voltage position 9/10 on the boiler which makes it stop heating the house and then it calls for 170 degrees to fire the water for the IDWH. Instead the aqua stat is only connected to the taco relay panel priority zone 6.
The installer used a Taco SR 506-6 zone relay. We keep running out of hot water and I discovered why.
I noticed when I looked at the control board there’s no wires in the aqua stat low voltage position 9/10 on the boiler which makes it stop heating the house and then it calls for 170 degrees to fire the water for the IDWH. Instead the aqua stat is only connected to the taco relay panel priority zone 6.
The problem is that when I run out of hot water and the hydrostat makes a call it only goes to the taco and not the boiler which causes the circulator pump to turn on and the taco makes the call to the boiler for radiant heat (which is based on the design temp for that day). So the boiler doesn’t know it’s suppose to be running hotter water to replenish the IDWH.
My question is how do I convey to them I need the Hydrostat also sending a signal to the boiler in the 9-10 position on the control module. Or is there a way to wire the Taco 506 to have an out put for house heat and an output for IDWH?
My question is how do I convey to them I need the Hydrostat also sending a signal to the boiler in the 9-10 position on the control module. Or is there a way to wire the Taco 506 to have an out put for house heat and an output for IDWH?
For some reason my installer wants to wire it like it’s my old 1976 boiler which I replaced and it was running great. I want to use this new boiler for maximum efficiency.
0
Comments
-
most mod-cons have the indirect wired direct to the boiler for this reason. do you have the wiring diagram for the boiler? it should show where the tank sensor and circ get wired in for the indirect so it overrides the outdoor reset.0
-
There is a better way to wire up the DHW pump and thermostat.
This will get you unlimited DHW.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Yes, as @EdTheHeaterMan said, basically the circulator wiring for the indirect needs to go back to the boilers X2 block, not the Zone panel.
0 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements