Furnace Help
Comments
-
We would need to know if there is voltage going to the gas valve during the cycle ..
There was an error rendering this rich post.
0 -
@mbinder... There are so many reasons for that. It could be that the control board (usually called a fan timer) is defective. But more likely there is a sensor or other item that is connected to the board that is not doing its job correctly.It is doing it's job and the reason for the failure to light must be fixed; like a blocked vent switch may not allow the gas valve to open until the thing that is blocking the vent is removed
OR
What model number is your AirTemp?
This way I can look up what control comes with that furnace and see what the trouble shooting guide says the cause might be.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
@EdTheHeaterMan It’s VG7SA 072C-24B1. Outside says Airtemp, inside the door says Nordyne. Thanks!0
-
It appears that your Fan timer control has 3 LED lights, a Green, a Red, and a Yellow. Is there a way to see those lights when the problem is happening?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
EdTheHeaterMan said:It appears that your Fan timer control has 3 LED lights, a Green, a Red, and a Yellow. Is there a way to see those lights when the problem is happening?0
-
The yellow is Proof of Flame.
Nothing flashing on the Red or Green. There is a solder connection on the under side of your fan timer that has eroded away. The wire that goes to MV on the gas valve comes from the 12 pin connector. One of those 2 yellow wires is not making contact. If you are handy with a soldering iron and you are comfortable with taking the Fan Timer board off the furnace, I bet you will find a bad connection on the 12 pin socket attached to that board.
If you are not a DIY then you need a pro to replace the fan timer. It will be priceyEdward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
The first thing you want to do is to make sure the yellow wires from the 9 pin connector are connected to the board and the gas valve.
With the power off
1. To do this you pinch the clip in the 12 pin connector and remove the plug. Then plug it back in
2. Then look at the yellow wires on the actual gas valve that is on the gas pipe. See that the connection to the gas valve is good.
3. Then turn the power on and try the heater again.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
EdTheHeaterMan said:The first thing you want to do is to make sure the yellow wires from the 9 pin connector are connected to the board and the gas valve. With the power of 1. To do this you pinch the clip in the 12 pin connector and remove the plug. Then plug it back in 2. Then look at the yellow wires on the actual gas valve that is on the gas pipe. See that the connection to the gas valve is good. 3. Then turn the power on and try the heater again.0
-
mbinder said:
Tried this. Nothing different. Still have power from board to gas valve, just seems solenoid isn’t firing. Seems like a bad gas valve?
As long as you are sure that the gas valve is getting 24 volts and not opening then you have the correct diagnosis. How did you verify the valve did not open with 24 V power to it? with an electric multi meter set to read AC volts?
The other way is to take 24 volts directly from a transformer and apply it to the valve terminals. When 24 Volts is present the valve should open.
And finally the real stupid question. Is there an on/off switch on the gas valve? Is it set to ON?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
EdTheHeaterMan said:
Tried this. Nothing different. Still have power from board to gas valve, just seems solenoid isn’t firing. Seems like a bad gas valve?
As long as you are sure that the gas valve is getting 24 volts and not opening then you have the correct diagnosis. How did you verify the valve did not open with 24 V power to it? with an electric multi meter set to read AC volts? The other way is to take 24 volts directly from a transformer and apply it to the valve terminals. When 24 Volts is present the valve should open. And finally the real stupid question. Is there an on/off switch on the gas valve? Is it set to ON?0 -
Have you replaced the gas valve yet?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
You did check the pressure to the gas valve, right?0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements