Zone still heating after thermostat turned way down below current call temperature level
potatoskater
Member Posts: 52
Newly repaired pipes and new circulator pump and everything was working (yay) then it kept getting hotter (boo). We usually heat at 60 and it is 72 downstairs, I checked the furnace and the zone valve has no voltage but the returns are hot hot hot. I just turned off the boiler, turned off the fuse to the boiler and turned both back on wondering it this might reset things. Then I grew impatient and just turned off the thermostat on that first floor zone. Any ideas?? Thank you!
What kind of zone valve ?
I had one that was leaking thru a bit and would continue to allow heat.
The valve actuator was closed, but the valve itself was a wee bit open.
Any other zone that caused the circulator to come on would cause heat to keep going into that "closed" zone. I managed to tighten down the valve body a bit, and the situation ended.
Maybe post a pic of your manifolds ?
Currently in building maintenance.0 -
I just replaced the pump and it seems to be running all the time. We do have one zone the garage that never is able to heat up to its target temp, just a poor design and leaky box with pipes in it..,(ugh) so it is likely that zone is always calling but when I went to check the voltage, no zone was at the call voltage,…should I open the zone valve manually and see if there is some debris stuck in there that can then get pushed on by?0
Taco GoldDave Carpentier said:What kind of zone valve ?
I just shut down the boiler for a little while to try to cool off a bit0
Is this what you are talking about?
Need more information to properly diagnose flow through valve when thermostat is satisfied. never answered the question about type of valve that's bypassing? if the problem started when you changed the circulator, perhaps the circulator pressure is greater than the valve can hold back? Contact Taco at 401-942-8000 and ask for tech support.Joe Mattiello
Taco Comfort Solutions0 -
Thank you all, UPDATE: I shut it off fir the night as it was hit in the house and coasted through to the next day. I opened the zone valve manually and then when I started the boiler back up I closed the valve and everything has been fine since. 60 degrees solid. I don’t know what happened , if the shut down was a reset of sorts, if the valve had been stuck open somehow, maybe by some debris that accidentally was introduced when I swapped in the new pump but so far..,if that didn’t work I was going to press the red reset button on the furnace panel but alas.,,smooth knock on wood sailing. Many thanks to everyone who “piped” in!1
Still holding,,,! 👍0
- 120 Geothermal