To much venting
RuffinoVino
Member Posts: 51
I have 2 Gorton #1 on a main run about 33' from the boiler. The other side is only 7' run from the boiler to the riser and it does not have a vent. If I had a 3rd #1 where I have the other 2 will I be allowing the steam to travel to that side of the house much faster causing the other side to now have slower movement of steam to those radiators?
1
Depends.. Charts and guides are useful tools but you won't really see the effects of change in vents until you actually do it. I have a saying: "ANY small change to a Steam system can make HUGE DIFFERENCES!" SO go slow. If I were you, add the main vent and then adjust radiator
By radiator with your Gorton or Hoffman Air vents to either slow down or speed up the timing. Mad Dog 🐕0 -
When you get to the point that the venting capacity is as much as with no vents installed (open to the air), there is no advantage to adding venting capacity.
For example if you use a 1/2" steel pipe for connecting the vents, it can pass 4.8cfm @ 3 ounces pressure. That amounts to 7 Gorton #1s at 0.7cfm or a little more than 2 Gorton #2s at 2.2cfm.
See pages 198-199 in "The Lost Art of Steam Heating" or page 10 of the Gill/Pajek study here:
https://heatinghelp.com/systems-help-center/balancing-steam-systems-using-a-vent-capacity-chart/
Judge for yourself.0 -
I have had five Gorton #1s at the end of a 32' long 2" main for a long long time now. My other main is something like 8 or 10' long =, also 2" and has a single Gorton #1.
The size of your vents depends on a few things, the size of the boiler for example.
If you add a vent to your longer main and cause an issue, then increase venting on the short main and keep going until you stop seeing changes.
I highly recommend to either time how long steam takes to get from the boiler to the end of the longest main or measure backpressure at the boiler accurately (DO NOT use a 30 PSIG gauge). And do this test with all of the piping hot. Start the boiler, let it get all of the steam piping good and hot and shut it down. 5 minutes later run the test. I'm betting you'll find you need more venting.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0
- 121.3K All Categories
- 84K THE MAIN WALL
- 2.9K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 417 Carbon Monoxide Awareness
- 40 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.7K Gas Heating
- 119 Geothermal
- 155 Indoor-Air Quality
- 3K Oil Heating
- 56 Pipe Deterioration
- 768 Plumbing
- 5.4K Radiant Heating
- 362 Solar
- 14K Strictly Steam
- 3K Thermostats and Controls
- 51 Water Quality
- 38 Industry Classes
- 73 Job Opportunities
