Is Propoly vent pipe ok to vent a Burnham SCG-3NI condensing boiler?

Mario25
Mario25 Member Posts: 3
Hi, I am planning on having a gently used older Burnham SCG3NI condensing boiler (discontinued in 2012) installed to heat a small apartment.   I don’t think Pro Poly venting existed when this boiler was made and it’s not listed as an alternative in the Burnham installation guide.   Obviously can just go the AL29 route but just seeing what options are available.   I believe these Burnham SCG’s are Class 2 if I’m not mistaken and Duravent Pro Poly site states it can be used for Class 2 and 4.   

Comments

  • HomerJSmith
    HomerJSmith Member Posts: 2,635
    Ask the manufacturer of the boiler.
  • kcopp
    kcopp Member Posts: 4,499
    Looks like a CAT3 appliance. stainless is your only option i see.
    If the Mfg does not have it listed on the install instructions then you by all rights are bound to that.
  • hot_rod
    hot_rod Member Posts: 24,106
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • GGross
    GGross Member Posts: 1,398
    That boiler looks like it is a cast iron non-condensing boiler?

    anyway from the manual
    "Do not use this boiler with galvanized, Type 304 or Type 316 stainless steel, non metallic or any other
    non AL29-4C® based vent systems
    ."
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,857
    edited February 2023
    MikeAmann said:

    Then what are you supposed to use?

    Use the AL29-4C products that are available from Selkirk or Hart and Cooley https://www.supplyhouse.com/Z-FLEX-2SVEPWCF0302-3-x-2-Z-Vent-Pipe-9784000-p
    https://www.supplyhouse.com/Z-FLEX-2SVEEWCF0390-3-Z-Vent-90-Elbow-9779000-p
    and a bunch more

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Lyle {pheloa} Carter
  • Mario25
    Mario25 Member Posts: 3
    Guys thank you.   Just want to be clear but this is in fact a class 2 condensing boiler hence the SCG nomenclature (self condensing gas).   These were pre Alpine models.   I honestly think you can use Propoly.   When they wrote the manuals for these Burnhams back in 2004 to 2012 ProPoly didn’t exist so therefore it wouldn’t be in the manual.    I’m going to run it by Burnham just in case.    ZFlex is my alternative which is steel and about 35% more in cost.     
  • GGross
    GGross Member Posts: 1,398

    Ok but you asked if you can use it, and the only manual available for that product says that you can't use anything that is not AL29-4c.
  • GGross
    GGross Member Posts: 1,398
    edited February 2023
    @Mario25
    you can read more on this brochure, but they don't make any claims that this is a truly condensing product, just that the heat exchanger mixes cool water with the water in the boiler. This is a sealed combustion non-condensing boiler

    SCG does not stand for "self condensing gas" it stands for "sealed combustion gas" as stated in the product brochure

    Polypropylene vent existed prior to 2012, I know because we sold it back then

    Category 2 appliance is what I think you are claiming this is, there is no such appliance as category 2, the label exists but to the best of my knowledge no such product ever existed on market, and Burnham makes no claim that this is a cat2 appliance.

    https://s3.amazonaws.com/s3.supplyhouse.com/manuals/1291132419651/41964_PROD_FILE.pdf
  • Mario25
    Mario25 Member Posts: 3
    My mistake.   I thought it was one their earlier versions of a self condensing.   I will just got with the z flex which is al29 and listed in their manual.     Better to be safe.   Thank you.  
    GGross