Sharing oil lines
Servicewiz_3
Servicewiz_3 Member Posts: 71
A while ago, I had received a drawing on how to share oil lines on (2) 2pipe burners. Could I get that drawing? Thanks
    EBEBRATT-Ed Member Posts: 20,481
    You should not share oil lines on a two pipe system if there is any lift in the piping system (oil level below the level of the burner pumps). If the oil level is above the burner pumps you can share oil lines in most cases.
    If the lines are shared with the oil level below the pumps the burners will fight each other for oil. And check valves will not fix this.
    You can use two suction lines and a common return line with two burners
  • STEVEusaPA
    Suntec, or Webster's website has instructions, and piping diagrams.
    What are the particulars of the job.
    Depending on that, most residential setups you can do one pipe, to each burner. Avoid return lines, skip Tiger Loop if you can.
    EdTheHeaterMan Member Posts: 12,506
    edited February 2023
    https://www.websterfuelpumps.com/pump_docs/LL4640.pdf. Sharing oil lines starts on page 4
    Suntec does not recommend sharing fuel lines with multiple pumps (burners). http://www.etscompany.com/suntec_pdf/Installation and Service Manual - Section III.pdf in this booklet starting on page III-10 there is a section called
    SERVICING NON-RECOMMENDED
    EXISTING INSTALLATIONS
    that gives you recommendations for pipe sizing.
    Further on page III-11 it covers two pipe installations.
  • Big Ed_4
    Big Ed_4 Member Posts: 3,551
    If the tank is lower on a one pipe system , I would use one tiger loop on the hot water heater just to keep the line primed all year long . They takes out the guess work out of the equation ...