Old steam trap ID
Thanks for the help.
Comments
-
The insides look like Hoffman, but I can't read the lettering on the cap to verify that. Can we get a close-up?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
-
-
Some sandpaper on the cap or on the trap should reveal a name or #0
-
Sometimes..the real old ones don't always have a raised bossing. Mad Dog1
-
OK. Thanks for the help. After cleaning off years of baked on lead based paint I found that it is a Hoffman #18. Now the question is how does it work as there are no bellows and more importantyly where can I find a replacement capsule for the best price (I have 17 of these to replace).
0 -
-
-
All Steamed Up, Inc.
"Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc3 -
Thought so. This is a Hoffman Vapor system. Is there, by chance, a Differential Loop in the basement near the boiler?Petemcl said:OK. Thanks for the help. After cleaning off years of baked on lead based paint I found that it is a Hoffman #18. Now the question is how does it work as there are no bellows and more importantyly where can I find a replacement capsule for the best price (I have 17 of these to replace).
ISTR the Tunstall repair kit may require replacing the cap on each trap. Their website was not specific though. The Barnes & Jones one can use the existing cap, which would not incur the extra cost of the cap. You'll want to check with Tunstall to be sure.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Thanks. Yes, I ordered a Tunstall capsule and cap from Athena in Chicago today. I didn’t order their install tool. Will I need it?Steamhead said:Thought so. This is a Hoffman Vapor system. Is there, by chance, a Differential Loop in the basement near the boiler?
ISTR the Tunstall repair kit may require replacing the cap on each trap. Their website was not specific though. The Barnes & Jones one can use the existing cap, which would not incur the extra cost of the cap. You'll want to check with Tunstall to be sure.
There is a trap in the basement that looks like it joins the steam side to the water drain side of the system. It looks different than the Hoffman 18 but it is in an awkward spot so it will take a bit of gymnastics to get to it.
Thanks again to everyone for the help.
0 -
If it was a hoffman differential system there is, or at least was, a deep u bend type of trap somewhere near the boiler that would equalize the supply and return pressure if the supply pressure got too high.0
-
That's a "Crossover Trap". Its job is to let the air from the main vent out quickly, which reduces the system's heating-up time, saving fuel. The air is routed into the dry (overhead) return and vented near the boiler. If the system has a Differential Loop, the vent is on top of it.Petemcl said:.......There is a trap in the basement that looks like it joins the steam side to the water drain side of the system. It looks different than the Hoffman 18 but it is in an awkward spot so it will take a bit of gymnastics to get to it.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements