CH set to 170 boiler doesn't reach it
TimmyLS
Member Posts: 7
Hey all, I have a wmb-155c NG boiler and its acting weird lately. I've set the heating water temp to 170 but when thermostat is calling for heat the boiler will briefly fire at "medium" (flame indicator on display) until it reaches 140ish and then go down into low fire and maintain right around that temp. It will stay on like that for quite some time as house isn't heating up enough to shut the thermostat off. Any ideas??
0
Comments
-
-
Kcopp thanks for the reply. There isn't an outdoor temp sensor installed on this unit. I've seen mention of it as optional in the manual.
Our house is fairly warm, 65, thermostat set to 68 though.0 -
-
Interesting, though by changing the CH +/- on the front panel doesn't that change that parameter? I have set it to 170 by doing that.0
-
Are you in the installers mode when you make changes? Usually there is a passcode required to change some parametersBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
hot_rod said:Are you in the installers mode when you make changes? Usually there is a passcode required to change some parameters
0 -
Check the sensors with an ohm meter, you could have one out of range.
The troubleshooting pages explain how to get into installer mode to read any faults. The control will know why it didn’t reach the operating condition. Could be too high of a delta, high flue temperature or other issues.
You either have to sit in front of it, catch it in the act, could be the call for heat drops off before it hits the programmed temperature?
or pull the info from the data logging function deep in the control menu, the history mode.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
hot_rod said:Check the sensors with an ohm meter, you could have one out of range. The troubleshooting pages explain how to get into installer mode to read any faults. The control will know why it didn’t reach the operating condition. Could be too high of a delta, high flue temperature or other issues. You either have to sit in front of it, catch it in the act, could be the call for heat drops off before it hits the programmed temperature? or pull the info from the data logging function deep in the control menu, the history mode.
I think this corrected my issue. Or at least solved one problem!
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements