Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
CI SqFt Radiation Sizing
wcs5050
Member Posts: 142
Trying to determine output. I’m using Burnham cast iron slenderized emitter chart as reference on these.
6 column, 24” high, 26 sections, at 180degF I’m getting 10k-13k btu but am unsure on my chart understanding. Maybe someone has a better chart.
Yes, that piece fired off the far radiator and no one has moved it. Someone had just entered the room as 6 others let go and said it sounded like a gunshot.


0
Comments
-
What a minute. What made this casting explode?0
-
Ice, brah. Shock and awe.Really though. We had a cold snap in New England last week and it dipped to -12degF. Power was out for 24 at this church.0
-
For 180degF water, 78sq ft x 170btu/sqft: 13260
👍0 -
-
Ho-oly!0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements