CI SqFt Radiation Sizing
wcs5050
Member Posts: 147
Trying to determine output. I’m using Burnham cast iron slenderized emitter chart as reference on these.
6 column, 24” high, 26 sections, at 180degF I’m getting 10k-13k btu but am unsure on my chart understanding. Maybe someone has a better chart.
Yes, that piece fired off the far radiator and no one has moved it. Someone had just entered the room as 6 others let go and said it sounded like a gunshot.


0
Comments
-
What a minute. What made this casting explode?0
-
Ice, brah. Shock and awe.Really though. We had a cold snap in New England last week and it dipped to -12degF. Power was out for 24 at this church.0
-
For 180degF water, 78sq ft x 170btu/sqft: 13260
👍0 -
-
Ho-oly!0