Weil Mclain HE 2 series 1

inspkerr
inspkerr Member Posts: 23
Hello, had to switch out the controller on 1991 HE-2 they are recommending a 1013-200 control. the manual for the new control is saying if I have a B&G 100 circulator on this system, I should also get a 120-volt isolation relay with one set of normally open contacts can you recommend a relay for this ? THANK YOU - Paul

Comments

  • JUGHNE
    JUGHNE Member Posts: 11,279
    RIB, Relay In a Box, use the 120 volt coil.
  • inspkerr
    inspkerr Member Posts: 23
    Thank you , can you specify a part or model of this RIB ?
  • JUGHNE
    JUGHNE Member Posts: 11,279
    RIBU1C single pole10 amp load with multiple coil voltages. You would use the 120 volt coil connections....tape up unused leads.

    Supply House. com. Mounts in a 1/2" KO. Led indicator when on.
    inspkerr