Don’t paint gas pipe
Comments
-
Uh oh......Not good. Depends how thorough and sharp the inspector is. I'd just be honest and tell him what you did. You could try a wire wheel but you might make it stand out even more. Try to wire wheel the underside and see how it turns out. Good luck. Mad Dog
1 -
Was this just on a whim? Or did someone else suggest it to you? Mad 🐕 Dog0
-
-
This is always a problem.
In MA all outdoor gas pipe must be painted.
But when do you paint? It's a battle you can't win.
I have piped gas and not painted it and when the inspector shows up they say "You know this has to be painted, why didn't you paint it? What do you think I am going to come back again? You will have to pay for another inspection"
or
I paint the pipe, them I here " you know that paint can seal up a leak. Why did you paint it before inspection"
Every town every inspector is different2 -
Any way to remove the paint?0
-
I'd use a Soda blaster.
Paint stripper.Wire wheel..0 -
I'd be gladly testing that at 90 PSI before I considered sandblasting it, especially in the structure. That's going to be absolute hell.
If the piping is even reasonably tight 90 PSI should be easy.
Make sure you completely isolate any appliances and the gas meter from the system before performing such a test.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
2 -
Chemical paint stripper would probably be the way to take it off. Pressure testing is probably the better option.0
-
Ok so follow up question on painting gas lines. Inspection passed and inspector said I could paint gas pipe any color I wanted inside and outside has to be gray. I want to paint it yellow because the house also has old galvanized plumbing pipe and gas service is new to the area. I heard of a knuckle head unscrewing a pipe for a clogged drain line that turn out to be gas line in MD somewhere. So question is painting gas line not allowed before testing because it can mask/seal a potential leak correct? Any advantage in taping the joints as to not paint them on the inside of the house when painting gas lines inside of the house ?1
-
Some inspectors think paint can seal a gas leak.
Also, although a lot of states allow galvanized pipe for gas here in Massachusetts they do not. Apparently, someone thought the galvanized coating could cover up a pipe defect and chip off later.
So every location has its kinks.
If you're going to or are required to paint gas pipe I would want paint on the threads because that is the most likely place to rust1 -
My experience working in NYC is:
•Paint on the line = 90 PSI test.•No galvanized pipe at all.•Stickers labeling the pipe natural gas every 6’These days they don’t want to grandfather anything. They want the whole gas system brought up to current standards anytime you’re doing a test.
It sounds like you got away with one here. I wouldn’t paint the piping any further. Put natural gas stickers on it to designate it.2 -
A 3 psi air pressure test rarely holds especially on large apartment buildings (Think The Projects)..Forget about 90 but it is worth a shot. It might hold or have a few small leaks to fix. This happened to once as as a brand new license master plumber. We paint ALL The black pipe on a new steam or hot 🔥 water boiler pipe and fittings with Black Magic Asphalt Paint (also used on lead bends and lead pans). We do this purely out if pride. In my exuberance I painted the gas drop from the ceiling only. 6 feet so it would have been an easy fix. My father in law met the inspector. I wasnt there: Inspector
"Beautiful job on the boiler but why'd ya paint the gas too?? Now ya gotta test the whole system at 90PSI!!!!!!" My father in law, who is still good with his mouth and fast on his feet at 78, (US Navy, live wire wisecracking guy who at his career apogee
Was Chief of Water Bureau for our Large County so he could spar with the best of them) Pops, quickly turned it around on the inspector "C'mon...you KNOW Triple Crown always paints all their black boiler pipe...the kid (helper) just went a little overboard with the paint. The counter attack worked...The inspectors wheels were spinning and it set him back on his 👠 heels. "Oh....yeah..thats right...just so I test soap test it for me right now and were good.!" Whew! Dodged a bullet...ha ha. Never did that again...mad 🐕 Dog1 -
Learn something everyday .....
My NJ projects -- galvanized outside per inspector ... wrap anything in the ground. Gas company paints what they do green.0 -
-
I used to believe that too but last heating season, I found a condensate return line leaking that I installed a few years ago. 1/2" black pipe bought from a big box store and cut to size. Turns out, at the nine o'clock position, there was a perfectly drilled 1/16" hole in the pipe. I didn't find it until I encapsulated my crawl space. Someone could have easily bought it and used it for a gas line.I've never had pipe leak. I've never even heard of a pipe leak. Sounds like an artifact.
1 -
SlamDunk said:
I've never had pipe leak. I've never even heard of a pipe leak. Sounds like an artifact.
I used to believe that too but last heating season, I found a condensate return line leaking that I installed a few years ago. 1/2" black pipe bought from a big box store and cut to size. Turns out, at the nine o'clock position, there was a perfectly drilled 1/16" hole in the pipe. I didn't find it until I encapsulated my crawl space. Someone could have easily bought it and used it for a gas line.
True,
But they would've find that hole very fast with a pressure test. A 1/16" hole, could you even pump up pressure using a hand tire pump with that size hole in the pipe?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
-
Unless like me you dry fit something when trying to figure out a complicated offset and forgot to take that section apart and re-fit it with dope and wrenchesSlamDunk said:Doubt it. Just saying there was a time when I thought good threads, good dope, good torque -no need to worry about 1/4 psi leaking out.
2 -
Seen many barely more than hand tight gas piping with the old gray pro dope still mushy...NOT leaking. Mad Dog0
-
@Mad Dog_2
We has a 600' run of 3" black screwed lo pressure gas we ran across our shop to feed 4 new roof top units in an addition.
When we tested it it leaked very slow at 100psi. You would watch the gauge and swear it was ok but the next morning it would be down 10psi or so. Finally found it. Drip cap on the riser to 1 of the RTUs was never made up was just hand tight. TG it was not the main.
Another time we subbed out some gas piping and the guys we hired couldn't find the leak and it was all welded fittings. They looked and looked and finally found the seam on 1 stick of pipe leaking. China pipe. That will ruin your day.
On more than 1 occasion we used to put a little referigerant in the pipe then blow it up with air and find the leak with a refrigerant leak detector0 -
-
For many many years, I never had a leak in any of the gas piping I did! I always passed the pressure tests the first time! Then one day, I installed a new gas furnace in a single-family home. I was collecting my tools and taking them out to the truck, while letting the furnace run to heat the house up. I stopped to check the furnace and suddenly heard a hiss and smelled gas! I shut everything down and started to re-check the gas piping. I found a brand new 1/2" elbow that had a casting hole in it! It hadn't leaked when I checked for leaks. But whatever was holding it together had opened up! Thank God it happened before I left the job!3
-
-
* Gingerly free-up, and work (and lube? as appropriate) all gas cocks, and unions wouldn't hurt to free the collars.Halharash said:I am getting ready for a gas pressure test in NYC. I spray painted a few feet of the gas line next to the meter to make it look nice.
Picture attached.Does this mean I have now committed to a 90 PSI test instead of the usual 3?Any recommendations on how to remove spray paint from gas pipe?TIA
* Set your test (start at 5# or as high as allowed) and call it a day.
* No need to bring the inspector's attention to anything.. forget about it.
* You can dry 'dirty' to dull the pipe with a rag just for the look of age to blend - lol.
0 -
What kind of pressure is the gas service in US??? Your discussion seems to indicate that you need to air test at 3 psi or 90 depending on whether painted or not which seems a bit silly on both ends (useless on one and excessive on the other). B149 (Canadian gas code) requires 15/15 in most residential and commercial applications. Painted or not. Mainline pressure is usually 60 psi, reduced to 7 inches wc (residential and some commercial) or 2 to 5 psi (fancy residential or most commercial). I have a hard time seeing what difference paint would make if you're testing at 60 x the service pressure.....0
-
-
I agree with you guys, but it's one of those "untouchable" subjects to some...Don't even go there!!! We did 3" and 4" Low pressure gas in the NYC Financial center, hundreds of feet of pipe. The Building wanted 35-400 p.si. more or less. I was duly a little nervous about leaks and KILLED the joints. Wheh!!!No leakers. Mad Dog0
-
If its existing pipe and you are doing a gas test, you should be fine depending on the inspector. If it is new pipe, try to justify with the inspector by using code 406.4.1.2 in the 2022 NYC Fuel Gas Code.0
-
How is low pressure testing more reliable at finding leaks?Bob Harper said:High pressure testing is stupid. 3 psi for residential more reliable at finding leaks. Painting should not make any difference in the testing.
I think the whole paint thing has to do with alleged claims that paint could seal leaks but then fail later. I get it, but it is a bit much.
I find it much easier to find leaks at 100 psi than I do at 3 psi and sch40 steel pipe with threaded joints should easily handle 150 psi. If it doesn't, something wasn't done correctly.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
4 -
-
I really resent having to go to Help-Yourself Depot...it. terrible Mad Dog
1 -
First of all, the IFGC/ NFPA 54 both call for 3 psi x 10 min. or 10x the maximum working pressure. Since most gas controls allow for 14 wci/ 0.5 psi that takes you to 5 psi. The test gauge cannot be greater than 5x the test pressure. At low pressure, that means a 25 psi gauge. At 90 psi, that's a 450 psi gauge. How big must a leak be for a 450 psi gauge's needle to move in 10 min. vs. the low pressure? The low pressure test is MUCH more accurate at finding small leaks. A large leak will be evident right away.
What if an unpainted pipe passes a 10,000 psi test then gets acid spilled on it? Does the high pressure test prevent changes to the piping? The test should be based upon the test conditions at the time. Painting protects the pipe. Sch. 40 pipe is not going to be adversely affected by surface corrosion. The paint inhibits further corrosion. Most shutoff valves are rated for 5 psi. The high pressure test can blow valve seats and bonnet seals thus causing a leak. You have to isolate appliance controls valves when testing > 14 wci. by disconnecting the piping and capping it.
2 -
Bob Harper said:
First of all, the IFGC/ NFPA 54 both call for 3 psi x 10 min. or 10x the maximum working pressure. Since most gas controls allow for 14 wci/ 0.5 psi that takes you to 5 psi. The test gauge cannot be greater than 5x the test pressure. At low pressure, that means a 25 psi gauge. At 90 psi, that's a 450 psi gauge. How big must a leak be for a 450 psi gauge's needle to move in 10 min. vs. the low pressure? The low pressure test is MUCH more accurate at finding small leaks. A large leak will be evident right away.
What if an unpainted pipe passes a 10,000 psi test then gets acid spilled on it? Does the high pressure test prevent changes to the piping? The test should be based upon the test conditions at the time. Painting protects the pipe. Sch. 40 pipe is not going to be adversely affected by surface corrosion. The paint inhibits further corrosion. Most shutoff valves are rated for 5 psi. The high pressure test can blow valve seats and bonnet seals thus causing a leak. You have to isolate appliance controls valves when testing > 14 wci. by disconnecting the piping and capping it.
I don't know about the 5X thing for gauges, but the way you worded that was the gauge cannot be larger than 5X. For me, testing 100 psi I'd want a 150 to 200 psi gauge.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
And then there’s the house at the Beach on a crawl space with the windows to the crawl space open and or missing!Thank goodness, we made up some of the pieces in the 300 with a wrench held back by hand , I swear, to feel the level of tightness.
Next morning after running all night after testing, the 1 1/4 “ galvanized fitting let go!!
Omg , glad those windows were there and no basement!!!Lesson learned, use a Vise !!!4 -
round here we test lo pressure gas at 3-5 psi unless the pipe lenght exceeds 100 feet then you must test at 100psi.0
-
I'm all for pressure testing, but I think the painted pipe = 90 psi test is a bit of overkill but, then again I've seen seasoned plumbers do some crazy things to pass a gas test. The foreman told these guys
"OK guys...you REALLY gotta kill these joints...we can't have no leaks!' The lead guy with the Long ponytail and missing front tooth was like. '...oh REALLY...ok..you got it..." They told the foreman they needed Black Permatex and ALOT of quikwick[Thin lamp wick). What??? You can't use wick on gas!!!!!! So, they did about 200' of 3" and 4' they wicked only the first half of the joint so no thread would show. They were right...not one leak. I would never do it, but they were right. Another time another company, the inspector caught a thread sticking out and made them take hundreds of feet, with numerous branches apart. Ouch! Mad Dog1 -
Long ago, the local AHJ made us test new gas lines with a mercury manometer. Now, it's with a glycerin-filled gauge. It just shows you how much the inspector's trusted the contractors. Perhaps with good reason.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
I have herd of contractors throwing a gauge on the ground to make it stick at the right pressure. Some inspectors around here want two gauges for that reason,0
-
EBEBRATT-Ed said:I have herd of contractors throwing a gauge on the ground to make it stick at the right pressure. Some inspectors around here want two gauges for that reason,
Two gauges seems ridiculous, you could just break both....
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
How much gas has to leak for you to be able to detect a leak on a 200 psi gauge? In the lab, they use a Bubble-O-Meter on gas valves to detect ultra low level leaks. A gas combination valve is tested to ANSI stds. allowing 235 cc/hr through the valve's main operator and 215 cc/hr through the seals of the valve. Humans can detect the odorant in the gas that equates to a level of about 1-2 ppm. This means a leak at a level of about an ounce per year. Not gonna see that kind of leak manifesting as needle deflection on a high psi gauge. Low level leaks are detected at ultra-low pressures. Medium level leaks are detected by low psi gauges. Very high pressure leaks can be detected by sound, smell, high psi gauges and the inability to even get up to test pressure on a low psi gauge. A leak that requires 89 psi will be so bad that you will easily detect it using lower pressure gear. It's simply stupid. All this does not require an electronic gas sniffer or anything else. High pressure testing endangers the public rather than protecting.ChrisJ said:Bob Harper said:First of all, the IFGC/ NFPA 54 both call for 3 psi x 10 min. or 10x the maximum working pressure. Since most gas controls allow for 14 wci/ 0.5 psi that takes you to 5 psi. The test gauge cannot be greater than 5x the test pressure. At low pressure, that means a 25 psi gauge. At 90 psi, that's a 450 psi gauge. How big must a leak be for a 450 psi gauge's needle to move in 10 min. vs. the low pressure? The low pressure test is MUCH more accurate at finding small leaks. A large leak will be evident right away.
What if an unpainted pipe passes a 10,000 psi test then gets acid spilled on it? Does the high pressure test prevent changes to the piping? The test should be based upon the test conditions at the time. Painting protects the pipe. Sch. 40 pipe is not going to be adversely affected by surface corrosion. The paint inhibits further corrosion. Most shutoff valves are rated for 5 psi. The high pressure test can blow valve seats and bonnet seals thus causing a leak. You have to isolate appliance controls valves when testing > 14 wci. by disconnecting the piping and capping it.
I don't know about the 5X thing for gauges, but the way you worded that was the gauge cannot be larger than 5X. For me, testing 100 psi I'd want a 150 to 200 psi gauge.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements