Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Tekmar Radiant Thermostat Replacement

CFS
CFS Member Posts: 2
edited January 2023 in Radiant Heating
Hello everyone. I've been having radiant floor heat issues in the bathroom and my plumber said its the thermostat but of course he did not com3 back to replace it. All in all i ordered the Tekmar replacement since my old one is discontinued 

Old thermo - tekmar 508
New thermo - tekmar 518

I think i matched up the wiring correctly but wanted to make confirm before i blow my system:

508 numbers 1 2 3 4 5 6
518 match  S1 = 1 COM = 2 C = 3 R = 4 Rh = 5 W1 = 6

Thanks in advance to everyone that responds


Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 7,828

    I hate it when they throw in an extra terminal. Away is not on your old thermostat
    Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics
    CFS
  • hot_rod
    hot_rod Member Posts: 22,120
    Your green and blue wires go on Rh and W1. Dry contact
    Red and white on C and R (red). 24v power

    Two white sensor leads on Com and S1 sensor

    Just don’t mix up the whites😁
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    CFS
  • CFS
    CFS Member Posts: 2
    Thanks so much Ed! I had it exactly as you stated which is a relief! I also hate the extra terminal but figured the no power terminals aren't going to damage anything if I had them reversed! Thanks again! Cheers!