Could this be why cast iron radiator not heating?
Dairon421
Dairon421 Member Posts: 81
I traced down the piping to the basement and I found that the supply  is on the radiator 90 (right side)and the return is the radiator valve(left side).  All the radiators are heating besides this one.I  purged out the air but my question is if the supply pipe and air purger on same side would it still be air trapped in radiator?
    EdTheHeaterMan Member Posts: 12,508
    edited January 2023
    Did you get water to come out of that vent on the top right side of the radiator?
    If you did. then the water is that high. all the way across.
    Is the radiator valve open? In most cases the valve is on the supply side, but if the valve is open, it should make no difference. There are no arrows inside the pipes that tell the water which way to go. The water takes the path of least resistance. A closed valve or other blockage is what I might call resistance. The water will just go a different way.
    Dairon421
  • Dairon421
    Did you get water to come out of that vent on the top right side of the radiator? If you did. then the water is that high. all the way across.
    Yeah water came out
    Then the water is all the way up there
  • Dairon421
    Yeah kind of weird tho.  I thought maybe since the purger and supply was on the same side, water will fill up on that half of the radiator first and that will cause the water to come out but the other half of the radiator still have air. Only two cells get warm on the radiator
  • PC7060
    PC7060 Member Posts: 1,844
    edited January 2023
    The radiator is open all across the top so doesn’t matter which side the bleed valve is located.
    As Ed said, the valve is typically on the supply side of the radiator but it doesn’t matter for standard valve. Some brand TRV will chatter if the  flow is reverse. Don’t ask me how I know.  :D
    mattmia2 Member Posts: 17,485
    edited January 2023
    If only 2 tubes are heating you are getting some flow but not enough. i could be gravity flow in the runnout off the supply main rather than through the radiator (or from the return if the valve came apart and is blocking the inlet). which side is hot?