Zone Control Wiring
Alan (California Radiant) Forbes
Member Posts: 4,243
Everyone has their own way of wiring, even on a controller where they provide you a terminal for every wire. This installer sent 24 volts (both "R" and "C", large red and blue wires) directly from the transformer to the thermostats and then a return wire from the thermostat to the "W" terminal.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab
Two btu per sq ft for degree difference for a slab
0
Comments
-
Was there a picture to go with this?
Otherwise, It sounds like R toEveryone has their own way of wiring, even on a controller where they provide you a terminal for every wire. This installer sent 24 volts (both "R" and "C", large red and blue wires) directly from the transformer to the thermostats and then a return wire from the thermostat to the "W" terminal.
R w to W and C to C is what you would expect.
Makes more sense with the photo.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Someone thought they can wire a nest
There was an error rendering this rich post.
0 -
Looks like an additional relay involved also
Does it work?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Maybe but why .... It would be simpler to rip the board out and hard wire
There was an error rendering this rich post.
0 -
Looks like they just basically mimicked what it looked like when it was wired without the zone control.
There was an error rendering this rich post.
0 -
Not a relay. It's just a toggle switch for those who prefer toggles to unplugging a cord.hot_rod said:Looks like an additional relay involved also
Does it work?
This was installed by a company in California, early on in hydronics who were very good at marketing. They used large water heaters for DHW and radiant (via a HX), homemade expansion tanks, non-barrier tubing, non-ferrous pumps, no remote manifolds (all home runs to the mechanical room)..........8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Are you sure they didnt burn out some part of it0
-
Has this ever worked before the Nest Thermostats were installed? I think they used the correct T terminal for the W. And R is R where ever you pick it up from. Same for C... C is still C where ever you pick it up from.
Looks like there is custom wiring in order to confuse their competitors. Kind of a guarantee that the customer comes back to the original installer for service. "If the competition can't figure it out, then I guess we need to call the guys that installed it"
Sounds like Weil McLain parts. Can't use lower price generic off the shelf parts, Must use the Weil McLain part number or it won't work.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
There are no Nest or other wi-fi thermostats; simple setback ones that are not power stealing. Some installers like to power thermostats with a "C" wire so you don't have to change the batteries so often.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab1 -
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements