Lochinvar Knight xl

I have a Lochinvar knight xl boiler and are getting a no flame ignition lock out.

We get a flame for a little bit but then it cuts out.

I have confirmed that flame sensor, ignitor and integrated control (mother board) is working.

Gas valve was replaced a few days ago but still the same problem.

Any ideas why?

Comments

  • hot_rod
    hot_rod Member Posts: 23,392
    Check gas pressure, both static and when it is trying to light off. Check it it right on the gas valve taps.