I think the units for the tubing diameter is in feet but i still couldn't convert that to a common tubing size but the order of magnitude was right. This is why carrying units through your algebra and canceling them out is important. It also looks like it has parenthesis and variables used willy nilly which have a very specific algebraic meaning but isn't what is meant here which makes it very hard to interpret what was meant. It is a great concept but some editing by someone who understands what is meant and understands algebra would make it a lot easier to understand.0
-
.0086 is the volume of fuel in 3/8” copper tubing, .75 is a multiplier, based on what, I have no idea (probably based on their own testing).
Also .258+3 = 3.258
L =50' length
Q=.60 gph firing rate
H=4' Vertical height
Lift Job
V = (L * .0086 * Q) + (.75 * H)
V= (50 * .0086 * .60) + (.75 * 4)
V= (.258) + (3)
V= 3.258
Gravity (tank above burner)
V = (L * .0086 * Q) - (.75 * H)
V= (50 * .0086 * .60) - (.75 * 4)
V= (.258) - (3)
V= -2.742 (no vacuum, not factored in-filters, valves, etc).
There was an error rendering this rich post.
0 -
I was taught a long time ago that 10 ft of horizontal 3/8" tube = 1" vacuum
every foot of lift above the oil level was about 1" vacuum. So the 50 ft plus the 4 ft would be about 9" vacuum. I think that was for 2 pipe systems. I know that on a single pipe system the fuel flows much slower, so the friction loss in that 3/8" tube is much less.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements