Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Mastertrol Mark V

I know its an old system, but trying to make it through the winter and get a new furnace next summer. The issue is, when zone 2 thermostat is turned on, the furnace will start up and start heating the house. After a random amount of time, the flame shuts off on the furnace, but the fan continues to run. Then zone 1 will not heat anymore. Shutting off the power to the furnace for a minute, resets everything and it go through the same scenario as above.

I replaced the zone 2 thermostat and still had the same results. Shutting off zone 2, allows zone 1 to operate normally. Shutting off zone 1 and running only zone 2, results in the same scenario again.

Any suggestions?

Thanks!