Help with sludged ignitor
josephny
Member Posts: 274
in Oil Heating
I just bought a small house with a Miller/Nordyne CMF2-80-PO-CONV furnace with Beckett AF-15 oil burner.
The unit was working fine for the first couple of weeks and then stopped.
I troubleshooted oil flow and then took out the nozzle/ignitor assembly and found the nozzle, and the tube that the nozzle screws on to, covered in oil sludge.
I didn't have a new nozzle, so I cleaned everything as best I could with acetone, reassembled and now it works.
One thing I discovered is that there is no filter on the oil line. Nor is there a shut off valve on the oil line.
The tank is outdoors and underground and copper tubing (feed and return) run from tank to furnace.
Am I correct that those things would be smart to put in?
If so, what is the best way to set it up?
Should I use hard brass NPT threaded pipe out of the furnace to support the filter case, then a nipple to a valve, and then back to tubing?
What I'd really like is a valve that has NPT on 1 side and flare for tubing on the other (I don't have much experience with flairing).
Am I correct in my usage of NPT and flair?
Lastly, the current nozzle is a 60-80 (which, I believe, means 0.60gph and 80 degree spread). Should I replace with the same spec or different?
Thank you very much!
0
Comments
-
Most mobile home oil furnaces are not equipped with an oil filter unfortunately. The oil pump strainer is the only thing to protect the nozzle. I like to install a Tiger Loop Ultra on these furnaces. It adds several benefits to keep the burner running right and the braided flexible oil lines make installation simple. You will need to add a bypass plug into the oil pump. The Tiger Loop Ultra also includes a firomatic valve that can be used to shut off the oil to the burner, but a ball valve with flare connections is better for service use.0
-
Wow, the Tiger Loop Ultra looks great. But now I'm wondering where I could fit any filter inside this cabinet.
0 -
I usually install them in the top left or right corner, above the burner. On yours I would go with the left side near the power cord for the burner, more room there.0
-
Unfortunately there's no feasible way to do a combustion test on those furnaces without going on the roof, which I think is total BS. IMO, they should provide a test port.
The nozzle needed should be listed on the door. They might list 2 firing rates. The pump strainer should also be replaced, and if using kerosene, the cause of the sludge should be found.
I've never had a sludge problem on a Miller firing kero without a filter.1 -
Wow, thank you guys so much for your help!
I will order a Tiger Loop Ultra.
Would anyone know exactly what to call the adapter from threaded valve (the one that comes with the Tiger) to copper flair?
Looks like Beckett has a complete bundle (Tiger Loop, valve, hoses, filter, mount) -- S220-12
Looks like I will need to cap off the current oil return line, right? Flair plug/cap?
0 -
I searched and scoured and I don't see a pump strainer on the unit or in parts diagrams.HVACNUT said:Unfortunately there's no feasible way to do a combustion test on those furnaces without going on the roof, which I think is total BS. IMO, they should provide a test port.
The nozzle needed should be listed on the door. They might list 2 firing rates. The pump strainer should also be replaced, and if using kerosene, the cause of the sludge should be found.
I've never had a sludge problem on a Miller firing kero without a filter.
I did find that the recommended nozzle is a 60-80A.
I haven't put any kerosene in the oil tank.
Are you suggesting that I don't need a filter?
Thank you.0 -
Usually it's recommended to run kerosene on mobile home furnaces. It tends to be burn cleaner and is less prone to some of the issues that go with regular #2 fuel oil. However I have heard its a little more expensive. You can cap off the return line if you go with the Tiger loop. The strainer is a standard Suntec strainer for the A2VA-7116 oil pumps and Beckett clean cut pumps. I believe the adapter you are looking for is a 3/8" NPT x 3/8" flare adapter. Sometimes I can clean up those pump strainers with a little carburetor or brake cleaner. If it's really sludged up just replace it.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements