Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Questions on venting
CaptPaul
Member Posts: 14
in Oil Heating
I have just started taking care of an oil-fired single pipe steam system with an old but dependable boiler. I can find no vents other than those on the radiators. The current air valves are mis-matched. A couple of them hiss. I have only 5 radiators all of which are old tube type. I have basically 1 small (23” with 7 sets of 4 tubes) and 4 large (38” and between 7 and 9 sets of 5 tubes). The thermostat is in the room with the largest radiator. The boiler is in the middle of the hour with radiators on the perimeter. They are basically equi-distant from the boiler.
I am looking for input as to how to determine what valves I should buy. I’m thinking maybe something like 3 Gorton #5’s and 2 #4’s for the small radiator and the thermostat room. I’m also thinking maybe adjustable valves on all 5.
Also, can I or should I think about putting venting on the lines?
Any input would be greatly appreciated.
I am looking for input as to how to determine what valves I should buy. I’m thinking maybe something like 3 Gorton #5’s and 2 #4’s for the small radiator and the thermostat room. I’m also thinking maybe adjustable valves on all 5.
Also, can I or should I think about putting venting on the lines?
Any input would be greatly appreciated.
0
Comments
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements