1890 Victorian house museum: sizing main vent
NealJ
Member Posts: 43
Looking for help checking/sizing the vent at the end of the steam main. Original was a Dole 1933 with a 3/4” male inlet. I have 52’ of 3” pipe and 23’ of 4” pipe between the ‘original’ header and the end of the main where the vent is located. See attached sketch (sorry, I’m not a draftsman). Any recommendations are appreciated. Thanks!
0
Comments
-
That Dole vent is pathetically inadequate. It had to have been meant for venting an individual convector. Build a manifold of 3/4" pipe and tees, and install 5 Gorton #2 vents. Then watch how much better it works.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks so much for your input. I found ‘Balancing Steam Systems and how to use the vent capacity chart booklet on this site. I’ve turned the system pressure down to the .5 to 1.5 pressure range and I’ve ordered 3 Gorton #2’s to start (at over $100 each, I’ll take my time). I do all of this work on the museum and I volunteer my time, and I also donate all of my maintenance costs, so it adds up to a lot!3
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements