Rattling flow control valve
Steve_210
Member Posts: 664
Installed about 10 years ago I know there’s a reason but I can’t remember why.
I backed it off enough so the noise would stop but maybe nowI will get Some gravity circulation.
If it rattles you have air going through it0
check whatever air removal device you have. Purger float vents plug or get stuck after time.Bob "hot rod" Rohr
Living the hydronic dream0 -
OK thanks there’s a Spirovent there I will check0
Hot Rod & Ed, do they ever rattle because of low water flow not lifting the weight?0
Mostly air related. The air does not have the same specific gravity as the water, so the air flow going by the valve allows the weighted valve component drop. Think of this like a saw blade pushing up on the metal floating valve actuator. Bubbles are like the low spot of the saw blade, the water is like the high points of the blade. If you have all air, the valve will not open very much (only enough for the air to pass), if you have all water flowing, the valve will not close.JUGHNE said:Hot Rod & Ed, do they ever rattle because of low water flow not lifting the weight?
Get rid if the air and the noise will stop.Edward Young Retired
Also, they will rattle if piped too close to a tee or 90. You end up with turbulent flow.To learn more about this professional, click here to visit their ad in Find A Contractor.0
Over 10 years old I backed off the flow control valve a few turns and noise stopped it was late at night I need to go back for a boiler service
I have seen that issue with turbulent flow0
- 129 Chimneys & Flues
- 122 Geothermal