Tekmar 361 not firing boiler

When the tekmar controller requires hot water, the burner indicator comes on but the condenser boiler isn't firing.

The system controls a Honeywell motorized port valve, which seems to be working ok but the signal isn't reaching the boiler.

The Honeywell seems to be opening on demand though, so am I right in thinking that there must be an issue boiler end, and that the contact there isn't closing?

Cheers

Comments

  • HVACNUT
    HVACNUT Member Posts: 6,282
    edited December 2022
    What model Honeywell valve?
    What make and model boiler?
    Pics?
    Is the Honeywell valve sending 24v to terminals 1 and 2? 
    Anything happen if you jump 9 and 10?
  • SavUK
    SavUK Member Posts: 14
    Just checked, the valve isn't opening. Must be a fault on the box, rather than the boiler or valve
  • SavUK
    SavUK Member Posts: 14
    edited December 2022
    I'm in the uk, so really is a Kanmor 361e. European version!