Tekmar 561 Help Please

vishal815
Member Posts: 4
Hi, I am trying to replace Tekmar One stage setpoint control 150 to Tekmar 561 wifi and need help with wiring.
Tekmar 150: C-, R+, Com, N/O, sensor 6, 7
Tekmar 561 has C, R, Away, Rh1, W1, Sen Com, S1, S2
Anyone knows about this? Which wire from 150 goes to which slot on 561?
Tekmar 150: C-, R+, Com, N/O, sensor 6, 7
Tekmar 561 has C, R, Away, Rh1, W1, Sen Com, S1, S2
Anyone knows about this? Which wire from 150 goes to which slot on 561?
0
Comments
-
0 -
0 -
Called tekmar (Watts) and they were a great help. C- -> C; R+->R; Com-> Rh1; N/O->W1; 6->Sen/Com; 7->S1. Did verify to make sure it's low voltage system.
Worked like a charm.0