circulation pump differences
jeff3176
Member Posts: 9
Hello all! Looking for any help regarding circulation pumps on my system. My upstairs zone has a Taco pump rated at 23gpm max. My basement zone has a grundfos pump, looks like its rated at 15 gpm max. My Taco pump is getting noisy, so I want to have a replacement on hand. I can get a Grundfos 3 speed with check valve locally, but I have to order the Taco. Can the Taco be changed to a Grundfos, or does the gpm matter? Thanks!
0
Comments
-
You should be able to change the Taco to a 3-speed Grundfos 15-58. I doubt that your upstairs zone needs a lot of gpm, but the pressure drop will determine what speed you need. What kind of heating do you have? Radiant in the floor? baseboard? fan coils?
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
For one, I doubt you would need 23 gpm for the upstairs zone of your home nor could you get that much anyway. Flow is determined by the amount of radiation in the zone and then the pipe size.
3/4" pipe can safely handle 4 gpm, 1" = 9gpm, 1-1/4" = 14 gpm..... Having a circ that can do 15 gpm in a zone that needs only 4 doesn't get the heat there any faster or better.
Its just oversized and that's it. Oversized circs are detrimental to the system performance.
Now there are circs available today that are variable speed and can be setup (there is no magic in them) to the application and needs of the system.
The flange to flange distance is the same and they are interchangeable.
Dave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements