Out of the 2 parallel piping option in the images, is one better then the other in terms of balancing flow and ease of piping?
Looking at a job replace 2x 80 gallon indirect DHW tanks. Currently piped with split Tee's, but I'm wondering if reverse return is better.
Just looking for opinions.
Thanks
0
Comments
-
JMHO but I like the RR. But I would put something on each tank to balance with.0
-
How are the coils piped from the boiler? These methods show balanced flow on the boiler and potable side. Balance valves allow you to dial in exactly the same flow rates.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
hot_rod said:How are the coils piped from the boiler? These methods show balanced flow on the boiler and potable side. Balance valves allow you to dial in exactly the same flow rates.
Tekmar 275 in control0 -
EBEBRATT-Ed said:JMHO but I like the RR. But I would put something on each tank to balance with.0
-
The Quicksetters are ideal for that use. The Quicksetter+ is the low lead version for the potable side. The readout meter is on the valve.
Pull the ring, set the flow. The flow does not go through the window, so it stays clear and clean for any future readings or adjusting.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements