Gravity flow in Indirect tank supply line?
PC7060
Member Posts: 1,431
The supply line that feed the cold water in for the HTP indirect tanks along with port on the Caleffi Angle Mixer valve gets very hot.
Is is possible there is gravity flow through the angle valve down into the input of the tank?
Or is this just conductive heating of the copper pipe after a Indirect tank heating cycle?
Or is this just conductive heating of the copper pipe after a Indirect tank heating cycle?
0
Comments
-
-
-
I thought so but was hoping @hot_rod would chime in.mattmia2 said:Is that a version of the mix with built in check valves?
"The mixing valve also features a thermal shut-off function that operates in the event of a cold water supply failure at the inlet."
Just read the description at supplyhouse.com - I think it just has the cold water fail safe cutoff
I checked it a bit ago and the temperature is warm but not hot. II expect the high heat is correlated with the boiler Indirect heating cycle. I'm finally insulating those pipes which will mitigate the heat loss.0 -
-
hot_rod said:How far away can you feel the temperature, conductive transfer in a copper tube can travel a foot or more That valve does not include checks, they are optional. A loss of cold will. Cause the valve to slow to a trickle.I can put a check valve below the T connection to prevent the counter flow.Any suggestions for high reliable valve? Preferably one that can serviced as required.0
-
If the check valve is only on the cold to the mix, not on the cold to the tank, do you need an expansion tank on the dhw?0
-
We have check valve tailpieces, but it looks like it is too tight to get them in now.
We also have serviceable checks that are NSF listed for potable waterBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
@mattmia2 - The check would need to block the counter flow from the supply side of the tank up though the cold water T . Which would block expansion through the cold water line which I guess requires an expansion tank somewhere between the check valve and the indirect tank? Ugh.
@hot_rod - thanks for the info, the NA51 looks like a good option if I’m willing to deal with addition of the expansion tank.0 -
-
@Larry Weingarten - thanks for the tip, interesting read, looks like a squared off S trap.I’m going to install a heat traps on both input and output lines. Is there minimum dimensions to the down leg for the trap to be effective?I assume a 6-8” down leg on 3/4” line would work fine.Thanks in advance and have a great Thanksgiving!0
-
Hi and yes, the minimum trap depth should be six inches, but if you have much height above it, (like multiple stories), there is no harm in making it deeper. It would be fun to make a foot deep trap and watch it with an IR camera to see what happens ... Then insulate it!
Yours, Larry
ps. There is plenty to give thanks for. Thanks!
1 -
Thermal traps used to be common, but you rarely see them anymore, not even in installation manuals?
possibly since the Neopryl checks in the valve or tailpieces became more mainstream.
The ASSE listing required checks on the 1070 valves
https://www.esbe.eu/storage/A954F7A4893264CFD136A33C4713D222C90A26C1479162354272646E5F92447A/9829930462e4474dbb7e22417c5b2611/pdf/media/6acdc116fef7420092634779f2ed6a1b/Heat%20traps%20in%20installations%2020120508.pdf?forceDownload=true
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I had a water heater with those heat trap flow valves built in to it. It has been gone for about 4 years and i still expect that clicking back and forth a couple times every time i turn off the water.0
-
-
All - Thanks for the information.
@MikeAmann - i saw those preformed traps at supply house tonight by unfortunately both of my traps will need to be installed on vertical runs so I’m going to order a box of press-90 and make on site. I’ve got plenty of 3/4 pipe scrap so should be about to make two for about same price as two of the pre-fab ones.@Larry Weingarten - I’ll be sure to borrow the Fluke IR camera from work and get a few screen grabs of the action!
@hot_rod - I had one of your Caleffi check valve in the cart, but decided to give Larry’s idea a try so I could avoid adding an expansion tank to my system. I expect the traps are gonna get some looks from some future plumbers!2 -
Added the heat trap per @Larry Weingarten recommendation on the hot water line exiting the Indirect Tank and it works like a treat! The convective movement of the hot water is completely stopped at the top of the trap with cold accumulating at the bottom.
I decided to leave the cold water supply pipe as is since the issue I originally noted occurs infrequently and the movement of the hot water is from the lower port back into the tank via the upper port. Insulating the pipe has mitigated the heat loss of the flow when it occurs.1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements