How should I add a low temp in floor loop to a 180º manifold system.

virtualplumber
Member Posts: 35
I have a 4-zone manifold that serves a baseboard system. I want to add two new in-floor loops that will need to run at low temps. The current system is not a primary loop design. It is a simple 4-zone manifold with return lines on each zone. How do I temper the new zone?
0
Comments
-
Small radiant loop, You will need to add a circulator pump for the radiant loop and a mixing valve. Inexpensive taco 007 pump is fine for this.
If you are zoning with circulators the piping diagram is similar.
You may need to add a circulator relay, or get the circulator with the relay built in.
Edward Young Retired HVAC Contractor & HYDRONICIAN Services first oil burner at age 16 P/T trainer for EH-CC.org0 -
Thanks for this. I was hoping that I did not have to create a primary loop. What mixing valve would you recommend? Will the second loop ever be isolated from the expansion tank creating an issue? If so should I add a second expansion tank to the new loop? I want to add two small radiant loops. One for a mud room and the other for a small bath. I will use two zone valves for these. Should I use the Taco with the relay? If so will I need a separate transformer for the zone valves?0
-
Other options , so you don't series pumps
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I added a drawing of the actual layout below.0
-
Will this work?
0 -
This will work better. if you are showing the 2 blue tubes are return from the floor only. By placing the low temperature returns closer to the mixing valve C inlet, you will get better low temperature control.
are there 2 low temperature zones?
That means 2 zone valves and 2 thermostats and something to operate the low temperature pump.
if both loops can be on the same zone, then all you need is the pump.
I have had success with the AM101U mixing valve from Honeywell. try this one https://www.supplyhouse.com/Resideo-Braukmann-AM100-US-1LF-1-2-Lead-Free-Union-Sweat-Mixing-Valve-70-145F
Also available in union PEX and Union FPTEdward Young Retired HVAC Contractor & HYDRONICIAN Services first oil burner at age 16 P/T trainer for EH-CC.org0 -
Will this work?
0 -
0
Categories
- 120.2K All Categories
- 83.6K THE MAIN WALL
- 2.8K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 414 Carbon Monoxide Awareness
- 29 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.6K Gas Heating
- 114 Geothermal
- 151 Indoor-Air Quality
- 2.9K Oil Heating
- 49 Pipe Deterioration
- 735 Plumbing
- 5.2K Radiant Heating
- 355 Solar
- 13.8K Strictly Steam
- 3K Thermostats and Controls
- 50 Water Quality
- 36 Industry Classes
- 69 Job Opportunities
- 14 Recall Announcements