Optimizing my indirect-fired domestic hot water storage tank
skiereric
Member Posts: 66
I have a primary secondary setup where DHW has priority. I have spent a lot of time researching, but have come up empty on what is an optimized setting for DHW.
I feel the boiler is responding to a call quite often for DHW, which interrupts the heating call.
Here are the facts.
4000 square foot home, broken into two apartments, with a total of six people.
The boiler is a Weil Mclain 97+ 155.
The capacity of the indirect-fired domestic hot water storage tank is 51.3 US Gallons
The variables I can adjust are
-Boiler Supply Temp - Currently set to 185F
-Circulator Speed (UPS 26-99 FC)- Currently set to High
-Mixing Valve - (Adjusted to provide 115F water)
-Emerson Type 11B76 - 4 Aquastat with a fixed 4F differential with a dial with a setting between cold, norm,hot - I am at "norm"
Any thoughts on adjustments that could be made to reduce the number of calls for DHW? or any other steps I can take to gather more data?
I feel the boiler is responding to a call quite often for DHW, which interrupts the heating call.
Here are the facts.
4000 square foot home, broken into two apartments, with a total of six people.
The boiler is a Weil Mclain 97+ 155.
The capacity of the indirect-fired domestic hot water storage tank is 51.3 US Gallons
The variables I can adjust are
-Boiler Supply Temp - Currently set to 185F
-Circulator Speed (UPS 26-99 FC)- Currently set to High
-Mixing Valve - (Adjusted to provide 115F water)
-Emerson Type 11B76 - 4 Aquastat with a fixed 4F differential with a dial with a setting between cold, norm,hot - I am at "norm"
Any thoughts on adjustments that could be made to reduce the number of calls for DHW? or any other steps I can take to gather more data?
0
Comments
-
A pic of the piping would help. Many installers prefer to take the indirect off the boiler as a parallel loop, instead of off the primary loop.
Then you get direct flow from boiler to tank for fastest recovery.
If the indirect is taking a long time to recover, the coil could be limed over reducing the heat transfer.
if that is a 155,000 boiler, it could
recover a 50 gallon tank in 10- 15 minuted depending on loads and tank temperatureBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
If you are getting a lot of calls for hot water that implies that you are using a fair amt of hot water.... any way to reduce the output? Lower flow shower heads? Dripping faucets?
0 -
A thermostatic mixing valve is a good upgrade for any water heater.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 918 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements