Honeywell VF06 feeder question

superxfly
Member Posts: 3
in Gas Heating
The boiler in my house has the Honeywell VF06 water feeder. There is a red knob on the bottom of it. Is that knob supposed to be open or closed in normal boiler operation? Thank you.

0
Comments
-
Instructions attached. They do not say which way to turn it. I would assume clockwise (looking from the bottom) would be off and counterclockwise would be on.
This is a controversy. Some will say (me included) to keep it on and some will say keep it off. Most keep it on.1 -
Thanks for the help. I did find this diagram of the valve and to me , it looks like it has to stay open.
0 -
The handle on the bottom is a manual on-off. The top controls the pressure setting. It does not have to stay on but that is the way they are most often used0
-
Look like a bad spot to install it , how can you service it ?
There was an error rendering this rich post.
0 -
That’s the way it was when I purchased the house. It will be a pain to service, but I’ll leave that to a professional.0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements