Boiler knocks when it starts
bwoodard28
Member Posts: 7
in Gas Heating
Hey all - my boiler just started doing this today.
It'll start up, knock around for about 30 seconds, shut off, wait about a minute, boot back up, and repeat the process.
Here's a video of it happening: https://photos.app.goo.gl/Unr3cDwSTcVWSHw89
Any help is greatly appreciated!
It'll start up, knock around for about 30 seconds, shut off, wait about a minute, boot back up, and repeat the process.
Here's a video of it happening: https://photos.app.goo.gl/Unr3cDwSTcVWSHw89
Any help is greatly appreciated!
0
Comments
-
That is a Laars design boiler. It has a copper heat exchanger across the top. You are not getting flow through the boiler. That sound is steam flashing inside the boiler because it is heating up so fast. More than likely the circulator has failed... I would not use the boiler until this is fixed.0
-
Agree with kcopp, however how does the steam hammer cause the flame to almost roll out?
The louder "knocks" coincide with the flame jumping.
How much pressure is in the boiler when cold?0 -
Dont those burners have an inner structure that sometimes disintegrates?0
-
kcopp said:That is a Laars design boiler. It has a copper heat exchanger across the top. You are not getting flow through the boiler. That sound is steam flashing inside the boiler because it is heating up so fast. More than likely the circulator has failed... I would not use the boiler until this is fixed.0
-
JUGHNE said:Agree with kcopp, however how does the steam hammer cause the flame to almost roll out? The louder "knocks" coincide with the flame jumping. How much pressure is in the boiler when cold?0
-
Raise the pressure to 12-15 PSI...cold.
See if the pressure holds there for about 1/2 hour....with no water on the floor.
You might then, cautiously, try another firing, with your hand on the power switch.
I have learned it is best to stand off to the side doing some trial run like this.0 -
Update: Replaced the circulator and it works like a champ now. Thanks for all the help!
PSI still reads at 5. Starting to think I have a bad gauge.0 -
@bwoodard28
If we attempt to connect the dots, a dead circulator, and a gauge reading low pressure. It sounds like perhaps you had a leak which would lower the pressure and add air, which could potentially have caused the pump to run dry causing premature failure. I would double check the pressure with a new gauge and make sure it is filled correctly to avoid repeating the same failure.1
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements