Boiler writing

valencia29
Member Posts: 7
in Gas Heating
I have a boiler with 6 zone using WHITE RODGERS 1311-102. All to individual thermostats. And a relay RA832A. The system only has one pump. I was wondering if I should have the burners and pump wired to the relay or should the pump be running at all times?
0
Comments
-
The circulator (pump) should never be running unless at least one zone is calling for heat (zone valve open). If you "dead-head" a circulator, it can tear itself up.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
So do u recommend I have both the pump and burners off the line side of the relay?0
-
-
I got the T-T going to the 6 zone valves wires in parallel. Wired like this diagram. My question is do I bring one of the loads from the relay to the transformer that feeds the boiler/burners? And the other load to the pump0
-
YES!
That way the pump and the burner will operate only when at least one valve is open.
There may be a time when only the pump will operate because the burner is off as a result of reaching the high limit aquastat setting, but that is fine.Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics1 -
Thank. Also if you can answer this just for my knowledge. On the relay RA832A what are the X-X terminals used for?0
-
Your wiring diagram indicates that you are using the WR 8A02A relay but you show a picture of the Honeywell RA832A relay. Since they are slightly different in the internal wiring I have prepared this diagram that may help in your rewiring.
X X on the RA832A is not needed in this application
Just be sure that the zone valve end switch is connected to TT on the RA832A relay. I believe that is probably the way it is already wired, bit check to be sure. The zone valve end switch is connected internally to terminals #2 and #3 in the zone valve.Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics1 -
Thank you 🙏0
-
Another thing to consider, With 6 zone valves, you will need a large 24 V transformer (like one rated at 75VA or more)... or there may be two 40VA transformers. Each transformer serving three valves. Be sure if you have 2 transformers serving 6 zone valves, that any rewiring will keep the transformers in phase with each other. ( that means do not reverse the R and the C on the transformers). Follow the same wiring scheme on all 6 valves. This is because #2 post on the valves is common to both the transformers on the valves and the transformer in the RA832A relay.
Swapping a wire on a system with one valve only, may work just fine, But swapping a wire on multiple valves and multiple transformers can put the transformers out of phase. If that happens, you will let all the smoke out of a transformer or two. Once you let out the smoke, you can't put it back in... You need to replace the transformer. But then if you don't correct the mis-wired circuit, You can let the smoke out of the new one. I find that using a 3amp auto fuse on a 40 VA transformer can save on smoking transformers.
Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics0
Categories
- All Categories
- 84.3K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 417 Carbon Monoxide Awareness
- 44 Chimneys & Flues
- 1.8K Domestic Hot Water
- 4.8K Gas Heating
- 120 Geothermal
- 156 Indoor-Air Quality
- 3.1K Oil Heating
- 57 Pipe Deterioration
- 799 Plumbing
- 5.5K Radiant Heating
- 371 Solar
- 14.1K Strictly Steam
- 3.1K Thermostats and Controls
- 54 Water Quality
- 39 Industry Classes
- 80 Job Opportunities
- 22 Recall Announcements