Noritz CB199DV boroscope video inside heat exchanger - is it bad?
Lost_aussie
Member Posts: 10
Hi
I got an error 11 (fail to fire) on My Noritz CB199DV combi boiler. Noted the flame observation ports are all gummed up with what looks like rust. I cleaned the flame detector observation port and replaced the gasket with the spare they shipped with it new- this has reduced the opacity and it's currently firing first try.
While I had the port open I took a video with my boroscope camera. Posting some stills below and a link to the video from my google drive. Does anyone have knowledge / experience to diagnose if I have an issue with the heat exchanger, or if this is normal. I did notice some popping / hissing on first startup, which makes me suspect moisture and perhaps a HX failure.
The full gory details of the 'inspection' video can be viewed at https://drive.google.com/file/d/1EdrEvcIZwLUdDnol7ud5xNQt7rKZRcll/view?usp=sharing
I'll be on the phone to Noritz tomorrow to hopefully get it resolved there, but wanted to get a trusted opinion (from the internet, not the manufacturer!!). Thanks in advance for any responses.
I got an error 11 (fail to fire) on My Noritz CB199DV combi boiler. Noted the flame observation ports are all gummed up with what looks like rust. I cleaned the flame detector observation port and replaced the gasket with the spare they shipped with it new- this has reduced the opacity and it's currently firing first try.
While I had the port open I took a video with my boroscope camera. Posting some stills below and a link to the video from my google drive. Does anyone have knowledge / experience to diagnose if I have an issue with the heat exchanger, or if this is normal. I did notice some popping / hissing on first startup, which makes me suspect moisture and perhaps a HX failure.
The full gory details of the 'inspection' video can be viewed at https://drive.google.com/file/d/1EdrEvcIZwLUdDnol7ud5xNQt7rKZRcll/view?usp=sharing
I'll be on the phone to Noritz tomorrow to hopefully get it resolved there, but wanted to get a trusted opinion (from the internet, not the manufacturer!!). Thanks in advance for any responses.
0
Comments
-
For anyone following along - Noritz initially said they'd replace the HX. However it's backordered, so they are replacing the entire unit with the NRCB199DV.
Install is at my cost. I installed the original unit, but will get it professionally replaced this time.0 -
-
That's actually a big win. Those heat exchangers do not look fun to replaceLost_aussie said:For anyone following along - Noritz initially said they'd replace the HX. However it's backordered, so they are replacing the entire unit with the NRCB199DV.
Install is at my cost. I installed the original unit, but will get it professionally replaced this time.1 -
It was not. Definitely amateur hour on the install (full disclosure, it was me). I have a professional coming to take care of the replacement on Monday.pedmec said:Yeah that's a lot of soot. the combustion process definitely not correct. was a combustion test done on start up?
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements