What is this device on my condensate return to a boiler feed tank?
860
Member Posts: 4
Hello, long time lurker, have taken Dans classes years ago. I’ve inherited a job site where I’m cutting my teeth and learning on a steam system that’s large by my residential experience.
A pair of Weil-McLane 88 boilers on a time sequence control, each rated at 1,084,000 btus. 7 pounds of steam. Each Carlin 702 has a single 5.50 nozzle at 350 psi on high fire.
Each boiler water level is managed by both a 63a low water cutoff at the lowest permissible water level and a bit higher up a 150s-md high pressure level control.
That control upon its low level will fire up the corresponding makeup feed pump from what is essentially a Skidmore duplex boiler feed tank of roughly 70 gallon capacity flooded.
That control upon its low level will fire up the corresponding makeup feed pump from what is essentially a Skidmore duplex boiler feed tank of roughly 70 gallon capacity flooded.
I also note that the 150-s has 3 distinct click sound positions when I manipulate the float buoy through its range of travel.
The condensate entering the boiler room is all protected by Hoffman type float and thermostatic valves in various parts of the building served by this steam plant.
The condensate entering the boiler room is all protected by Hoffman type float and thermostatic valves in various parts of the building served by this steam plant.
Condensate drains from the building, through this mystery object, then catches additional condensate drip from two more F&T valves within the boiler room, and lastly it all drips back into the feed tank.
In working out the bugs of this system, I’d like to know what this mysterious device is. Perhaps a swing check or pressure regulator. I have new bolts, nuts and appropriate gasket material so I’m about to take it apart to inspect it. Just wondering ahead of time if anyone knows what it is.
0
Comments
-
There is a name brand on the side of this device, located in a triangle. P & G Co. Or maybe P & C Co.I’m going to take it apart, clean, inspect. Resurface the flange and lid, cut a new gasket and reassemble. Given that there’s only 5 bolts holding the lid on, I certainly wouldn’t expect anything dangerous such as a large compressed spring.In your experiences, any ideas what it is?0
-
My guess would be a swing check valve. No Spring.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Thank you Ed. Definitely think that you’re right. I’m going to make sure that it’s in good condition when I return to service the F&T valves this week.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements