Heated water getting past circulators when heat is off
julianne_lynne
Member Posts: 13
Hey guys! First ever post but this issue has been bothering the heck out of me for far too long. I have a slant fin Liberty oil fired hot water boil w/ tankless coil. Domestic hw supply and 2 circulated heating zones w/ non-IFC taco pumps.
Boiler must maintain 180 degree min at all times for domestic supply.
In the summer, zone 2 piping is hot above the circulator pump while zone 1 is cold. Being that the writing on the black pump is upside down I initially though, duh. It was installed upside down. But then looked at the arrows on both pumps and both are pointing in the same direction.
In the summer, zone 2 piping is hot above the circulator pump while zone 1 is cold. Being that the writing on the black pump is upside down I initially though, duh. It was installed upside down. But then looked at the arrows on both pumps and both are pointing in the same direction.
I had 2 different companies come out (for quotes to install LWCO) and both said I needed to eliminate the flow chek and replace pumps with IFC pumps.
But I just haven’t been able to wrap my head around why heated water is getting past 1 pump and not the other!? I just noticed something odd though.. one of the pumps reads “WOB” above the arrow while the other says “HRT”
What do these abbreviations mean and why are they different? Or ANY other insights??
i should also note that while we have 2 zones- even if only zone 1 is calling for heat, zone 2 heats up to nearly the same temp regardless.
UPDATE:
hi all! I just wanted to thank everyone for their input! I ended up swapping out both circulators with IFC circulators and that seems to have solved the problem. I am now able to run the zones independently as well which is great and definitely helping with efficiency and oil consumption. Thank you all!!
What do these abbreviations mean and why are they different? Or ANY other insights??
i should also note that while we have 2 zones- even if only zone 1 is calling for heat, zone 2 heats up to nearly the same temp regardless.
UPDATE:
hi all! I just wanted to thank everyone for their input! I ended up swapping out both circulators with IFC circulators and that seems to have solved the problem. I am now able to run the zones independently as well which is great and definitely helping with efficiency and oil consumption. Thank you all!!
1
Comments
-
-
Thanks for the response! The flow check is on the completely opposite side of the system though and this occurs during the summer months when heated water is not being circulated through the system.See where the 2 zones converge below the circulator pumps and the large pipe goes into the boiler- of course the water sitting in that section of piping will be always be hot as the boiler must maintain its 180 deg. year round. But for some reason, and this is where I’m perplexed, the hot water is continuing to heat past (above) the circulator pump, while the other circulator keeps the heated winter contained. So it’s as if one valve were open and one were closed. However they’re both open and neither circulator has an internal flow check.I wish I could explain it better. Maybe I can post a video?0
-
And doesn’t it seem odd that the writing on one circulator is upright while the other is upside down? Just seems way too coincidental?
0 -
I am assuming there are two flow valves on the supply piping to each zone ? The one zone with the bypass , The flow valve needs to be cleaned . The bonnet has to be removed and the weight surface , the stem the weight rides on as well of the valve seat needs to be cleaned with fine steel wool .
There was an error rendering this rich post.
1 -
-
Ok thank you! That’s good to know. And I apologize I meant to post a picture of the entire system. I’ve added it to this comment below. Does the picture change your first response at all? I don’t know much but I’m I’m trying my best to learn so any advice at all is welcome and appreciated. I know the system is not right in many ways, I just can’t definitively explain why or how which drives me nuts. So I’m all ears!FC= Flow check
the thermal imager is just a pic from July showing how one zone is hot.0 -
You are experiencing a Phinomon called Ghost Flow (we get this a lot around the end of October). It is explained in this text bookhttps://documentlibrary.xylemappliedwater.com/wp-content/blogs.dir/22/files/2020/01/FH-Z100B-BG-Zoning-Made-Easy-2.pdf starting on page 10
The fix is to use a flow control valve on bo the the supply and return. You may be able to just purchase the check valve that fits in the existing pump. https://www.supplyhouse.com/Taco-006-047RP-IFC-Replacement-Kit-for-Select-Taco-00-Series-Cartridge-Circulators This one is supposed to fit the Taco 007-F5. It will not fit the older pumps since they were built before the IFC pumps were invented, but your pumps look to be the newer style.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
3 -
As far as the WOD and the HRT is concerned, they were cast in a different batch. The black one came with the boiler, the green one was purchased separately from the supply house stock. Both the same pump!
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2 -
I only see one flow valve , there should one be for each zone . To fix the mistake , either repipe the supply and add a flow valve per zone or add two spring check to each of the returns . Which comes with an IFC Taco . Since there is no problem with the circulators . I would just add the checks ..
There was an error rendering this rich post.
5 -
Big Ed_4 said:I only see one flow valve , there should one be for each zone . To fix the mistake , either repipe the supply and add a flow valve per zone or add two spring check to each of the returns . Which comes with an IFC Taco . Since there is no problem with the circulators . I would just add the checks ..Do you know if the circulators are on the correct side?0
-
EdTheHeaterMan said:You are experiencing a Phinomon called Ghost Flow (we get this a lot around the end of October). It is explained in this text bookhttps://documentlibrary.xylemappliedwater.com/wp-content/blogs.dir/22/files/2020/01/FH-Z100B-BG-Zoning-Made-Easy-2.pdf starting on page 10 The fix is to use a flow control valve on bo the the supply and return. You may be able to just purchase the check valve that fits in the existing pump. https://www.supplyhouse.com/Taco-006-047RP-IFC-Replacement-Kit-for-Select-Taco-00-Series-Cartridge-Circulators This one is supposed to fit the Taco 007-F5. It will not fit the older pumps since they were built before the IFC pumps were invented, but your pumps look to be the newer style.I would like to cut everything out and start from scratch to get it right. Unfortunately the 2 companies I had come out for quotes on doing so, we’re $2000 and have completely wrong info so I’ve been trying to determine the correct sequence. But the more I learn the less confident I become.Note;
For some reason, in the winter months, we’re unable to take a hot shower from start to finish. It will start off hot, cool off to Luke warm, then gradually get hot again, then luke warm, hot, repeat. In the summer it’s not an issue however I do close the valves on both zones during the summer.. not sure if that is relevant though?0 -
Boiler must maintain 180 degree min at all times for domestic supply.which means that you have a tempering valve in the domestic hot water sys. These valve need cleaning or replacing especially so in hard water areas and is most probably the source of the changing water temps when showering. The valve may be slow in responding to the changes in flow temperature. Just a thought.0
-
HomerJSmith said:Boiler must maintain 180 degree min at all times for domestic supply.which means that you have a tempering valve in the domestic hot water sys. These valve need cleaning or replacing especially so in hard water areas and is most probably the source of the changing water temps when showering. The valve may be slow in responding to the changes in flow temperature. Just a thought.0
-
With that much scale you definitely have a problem.i was EXTREMELY concerned about damaging boiler when I discovered the magnitude of rust but local HVAC pro told me it’s not possible to cause any damage or disruption internally, which I couldn’t wrap my head around.What he means is that the boiler is a closed sys. The boiler isn't open to the well water. What is the composition of that sink debris?0
-
HomerJSmith said:With that much scale you definitely have a problem.i was EXTREMELY concerned about damaging boiler when I discovered the magnitude of rust but local HVAC pro told me it’s not possible to cause any damage or disruption internally, which I couldn’t wrap my head around.What he means is that the boiler is a closed sys. The boiler isn't open to the well water. What is the composition of that sink debris?
the sediment is rust flakes from the well casing. The pictures are of what I removed from the whole house filter0 -
HomerJSmith said:Boiler must maintain 180 degree min at all times for domestic supply.which means that you have a tempering valve in the domestic hot water sys. These valve need cleaning or replacing especially so in hard water areas and is most probably the source of the changing water temps when showering. The valve may be slow in responding to the changes in flow temperature. Just a thought.0
-
Hi, Mixing and tempering valves are basically the same thing. They adjust in different ways to water temperature, so mix different ratios depending on what temperature you want and the hot and cold temps feeding the valve. Hope that makes sense.
Yours, Larry
PS limescale can really mess with the internal workings of these valves.0 -
A thermostatic tempering (or mixing) valve is required by most current plumbing codes for tankless coils. Before this requirement it was typical to install a globe valve bypass between cold and hot on tankless coils to temper the very hot water from the boiler, but with no thermostatic function.
After a lot of people got scalded…the code was changed.—
Bburd1 -
hi all! I just wanted to thank everyone for their input! I ended up swapping out both circulators with IFC circulators and that seems to have solved the problem. I am now able to run the zones independently as well which is great and definitely helping with efficiency and oil consumption. Thank you all!!
0 -
The Black Tacos come with the boiler Burnham,, Peerless,, WM et al . Their green , identical Taco green circs are supply house bought. Black 1978 Corvette stingray versus Green 1978 Corvette Stingray (yuck). No difference to a blind man. Mad Dog
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements