Anyone ever add a stack damper to a smaller Weil McLain LGB?

The Steam Whisperer
Member Posts: 1,287
It looks like all you would need to do is substitute an Ignition module with a built in damper plug for the first stage module and then install a harness and the damper. I'd say add a spill switch too. This would be for an LGB-7 or smaller ( standard 10 or 12 inch damper)