Aprilaire Duct Damper ?
Options

Richard D._2
Member Posts: 156
Long time not posting,
Hello all.
Been a Oil Tech over 45 years and retired 5+ years. SO things change in 5 years lol
I live in Maine my son is in Ct. call with a issue
Aprilaire Duct dampers I think Mod 6302 /6303
the belts are good !
Powered closed
Spring open
Dampers power closed but do not open when zone satisfied
2nd flr works sometimes
1st floor works by manual
Just told him to shoot a little WD 40 on the hinges and did have him clean the dampers
The damper Mtrs. look like Honeywell Zone Vale Motors
So a simple system but never worked on the brand, Last dampers I worked on were Trol A Temp
And I do have the manual on line
Fun trying to do a call over the phone lol
I assume if the spring is good it should stay open if the motor is out ?
The spring does have tension but I know springs can stretch and loose tension !!
Thanks for any help
Hello all.
Been a Oil Tech over 45 years and retired 5+ years. SO things change in 5 years lol
I live in Maine my son is in Ct. call with a issue
Aprilaire Duct dampers I think Mod 6302 /6303
the belts are good !
Powered closed
Spring open
Dampers power closed but do not open when zone satisfied
2nd flr works sometimes
1st floor works by manual
Just told him to shoot a little WD 40 on the hinges and did have him clean the dampers
The damper Mtrs. look like Honeywell Zone Vale Motors
So a simple system but never worked on the brand, Last dampers I worked on were Trol A Temp
And I do have the manual on line
Fun trying to do a call over the phone lol
I assume if the spring is good it should stay open if the motor is out ?
The spring does have tension but I know springs can stretch and loose tension !!
Thanks for any help
0
Comments
-
In my experience Aprilaire dampers are problematic. I would change them both to Honeywell or EWC. When ordering, the motor side is on the second measurement.0
-
Thank You.. I did not like them when I first saw them ,, Ill let him know .0
Categories
- All Categories
- 87K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 116 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 109 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 988 Plumbing
- 6.3K Radiant Heating
- 389 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 48 Job Opportunities
- 18 Recall Announcements