Viessmann pump replacement
Hey guys I have a viessmann 100 vitodens b1ha
The pump within the boiler grundfos ups 15-78 has failed which is kinda odd. Checking everything and don't know how it could just stop working. No garbage in pipes or nothing. I don't think its air because it worked fine until it didnt?
I could simply replace the head as I could've gotten a defective unit. But I figured I would upgrade it because the boilers circ is almost always on. (Still working out ODR setpoint and curve)
I have a grundfos alpha 2, and noticed it sips power compared to the ups 15 78.
Could I find an alpha 2 head and install it within the ups 15 78 body? The body is different but it has the same 4 screws to remove the pump.
I'm having trouble finding single parts so I may just have to get the whole alpha 2 pump and then use the head from it. (IF it's compatible)
Some info about my system is a 3 story house with floor heat. The boiler also heats an 79 gallon indirect.
The pump within the boiler grundfos ups 15-78 has failed which is kinda odd. Checking everything and don't know how it could just stop working. No garbage in pipes or nothing. I don't think its air because it worked fine until it didnt?
I could simply replace the head as I could've gotten a defective unit. But I figured I would upgrade it because the boilers circ is almost always on. (Still working out ODR setpoint and curve)
I have a grundfos alpha 2, and noticed it sips power compared to the ups 15 78.
Could I find an alpha 2 head and install it within the ups 15 78 body? The body is different but it has the same 4 screws to remove the pump.
I'm having trouble finding single parts so I may just have to get the whole alpha 2 pump and then use the head from it. (IF it's compatible)
Some info about my system is a 3 story house with floor heat. The boiler also heats an 79 gallon indirect.
0
Comments
-
Sometimes those Grundfos pumps have a different electrical plug.
Unusual for the pump to go bad. Can you meter how many amps it's drawing? Maybe see if it even has any power going to it. It may not be the pump.
I would only use the same pump as a replacement.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
I would remove it, power it up with a cord, see if it spins
The 15-78 is an OEM pump, I think it is still available, NTI still uses it. You can switch just the powerhead
If you can find the 15-78 curve deep in the Grundfos website, a 15-58 speed 3 may be close
In Grundfos terminology the 15 is the ID of the inlet opening, the second number is shutoff head in metric units
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I don't have an amp meter but a simple test light lol.
There is voltage to the head, I'm not sure if I can test the capacitor somehow but it isn't spinning or making any sound at all. It's like theres a break in the connection goinf to the actually motor internally
I figured instead of replacing it with the same style, I could give it an upgrade.0 -
Check and see the voltage on the pump, early Viessmanns
were 230 V and had step down transformersBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
It’s a fairly high head circ, probably to work the plate HX for DHW. It runs on speed 3
You would need to find a union body ECM to fit that spacing, possibly a Alpha 2 26-99
Not so easy to find union body circs in the US unless it is an OEM replacement
Plenty if online suppliers for that 15-78, and a wide price range!Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thank you guys! I replaced the pump with another grundfos ups 15 series pump0
-
Correction, it's set from factory to run at speed 3. Depending on installation, you might want to run the pump on speed 1, cause in that case you get better delta T as well as longer running times which is more energy efficient. Again, it depends.hot_rod said:It runs on speed 3
0 -
how do you figure that speed 1 will achieve a "better delta T"tamosius said:
Correction, it's set from factory to run at speed 3. Depending on installation, you might want to run the pump on speed 1, cause in that case you get better delta T as well as longer running times which is more energy efficient. Again, it depends.hot_rod said:It runs on speed 3
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements