Pump Sizing on Hydronic Heating in Garage
Atomsplitter
Member Posts: 3
So I've added a 26' x 35' attached garage onto the side of my house and I'm going to heat the floor with a Navien NHB-55 boiler. It's a single zone, primary-secondary system, with 4 equal length loops (234' each) of 1/2" oxygen barrier Pex. Navien manual suggests using a WILO Star 2 21 for the Primary loop circulator (althought another instruction they have they suggest a WILO Star S 16)?
The question I have is how do I calculate the pump requirements on the secondary side.
I have the heat loss and BTU requirements already calculated by the contractor that installed the Pex before the cement was poured, I'm just unsure how to calculate the pump requirements.
The question I have is how do I calculate the pump requirements on the secondary side.
I have the heat loss and BTU requirements already calculated by the contractor that installed the Pex before the cement was poured, I'm just unsure how to calculate the pump requirements.
0
Comments
-
-
Pretty much any circ in production will meet those requirements. If you're getting a 21 for the boiler loop, just get another for the floor and keep it simple.0
-
GroundUp, thanks for the reply,GroundUp said:Pretty much any circ in production will meet those requirements. If you're getting a 21 for the boiler loop, just get another for the floor and keep it simple.
I was wondering how the flow requirement was calculated?
Do I simply addd up all the required flows on the engineering calculation or is it more indepth than that?0 -
All the flow gets added together, but head loss does not rise beyond that of the highest loop. So in your case, the final number would be 3.8ft of head at 2.14 GPM according to the calc. Pretty much any circ will provide that. More flow never hurts anything with a garage radiant system, so the larger 21 circ would likely push about .8 GPM per loop and would better utilize all the BTU your boiler has to offer for recovery purposes IMO.0
-
Looks like the Star 16 is now a 17? But it seems to be a single speed.
A Star 5 is about perfect. A Grundfos 15-58 is another good choice
The Star 21 is a higher and steeper curve circ, the boiler must need that circ to overcome the pressure drop
In Wilo numbers the number is shutoff head, or the max head it can developBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
My suggestion, 0018e, I’m assuming you’re going with flow setters over telestats. If you are, you can control the flow in the circulator down to 2.14 Gal/min setting.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements