All 7 zones heat when any one zone calls for heat!

Summary 10/22
When any zone calls for heat, the (one) circulator pump operates properly, however all zones make heat. Only five of the seven four watts ¾ 200s-M5 flow check valves were replaced.

Update
10/22 11:07 Oops - My son just told me he only replaced only two check valves. MY BAD.

Heating Zones
#1 Hot Water Maker 80 gallon
#2 Master Bedroom – Cast Iron Baseboard
#3 Garage – 8ft Radiator
#4 Front corner Bedroom and Rear Corner Bedroom – Cast Iron Baseboard
#5 Radiant - Kitchen and adjoining Family Room
#6a Split Zone- Sunroom –Cast Iron Baseboard
#6b Split Zone - Available (not used)
#7 Available (no pump)
#8 Living room and Dining room - Cast Iron Baseboard

Mechanical Info.
Boiler- 2001 Utica DV200B 200,000btu
Boiler Controls – Replaced in 2009. Tekmar 260
Hot Water Maker – Replaced in 2017. Amtrol Boilermate CH-80Z
Primary Panel -2001 6 Terminals, Erie Zone Track SR601
Secondary Panel – 2001 3 terminals, Erie Zone Track SR301
4/22 Note: Five Grundfos UP15-42F zone pumps and four of the watts ¾ 200s-M5 flow check Valves were replaced.

Heating History
4/17/22
7am Zone #6 Sunroom: Thermostat manually set to call for heat. It is the only pump running. All zones were heating 25 minutes
9am Zone #1 Hot Water Maker: Runs for about 60 minutes; 2 Showers plus Laundry. Hot Water is the only pump running. All zones are heating. Temperature rises 4 degrees to 76 degrees in the entire house, outside temperature is 50 degrees.
4/18/22
Zone #6 Sun Room: Thermostat manually set to call for heat. It is the only pump running. All zones were heating in 25 minutes. Only Pump #6 is running
10/5/22
6am Zone #2 Sun Room: Thermostat manually set to call for heat. Master Bedroom: only pump running. All zones were heating in 25 minutes
10/6/22
6am Zone #6 Sun Room: Thermostat manually set to call for heat. Sunroom: only pump running. Heating Living room/Dining Room/Hall
10/21/22
9am Zone #2 Master Bedroom: Thermostat manually set to call for heat. Master Bedroom: only pump running. All zones were heating in 25 minutes. Outside temperature is 45 degrees.
12am Zone #4 Front Corner Bedroom and Rear Corner Bedroom: Thermostat manually set to call for heat. Corner Bedrooms: only pump running. All zones were heating in 25 minutes. Outside temperature was 52 degrees

Comments

  • neilc
    neilc Member Posts: 3,025
    post a general distant picture, or 2 from a second angle, of the boiler, circ, and valves, and piping to the ceiling,
    all in one shot,
    someone will see something