All 7 zones heat when any one zone calls for heat!
LearningFromTheBest1
Member Posts: 11
Summary 10/22
When any zone calls for heat, the (one) circulator pump operates properly, however all zones make heat. Only five of the seven four watts ¾ 200s-M5 flow check valves were replaced.
Update
10/22 11:07 Oops - My son just told me he only replaced only two check valves. MY BAD.
Heating Zones
#1 Hot Water Maker 80 gallon
#2 Master Bedroom – Cast Iron Baseboard
#3 Garage – 8ft Radiator
#4 Front corner Bedroom and Rear Corner Bedroom – Cast Iron Baseboard
#5 Radiant - Kitchen and adjoining Family Room
#6a Split Zone- Sunroom –Cast Iron Baseboard
#6b Split Zone - Available (not used)
#7 Available (no pump)
#8 Living room and Dining room - Cast Iron Baseboard
Mechanical Info.
Boiler- 2001 Utica DV200B 200,000btu
Boiler Controls – Replaced in 2009. Tekmar 260
Hot Water Maker – Replaced in 2017. Amtrol Boilermate CH-80Z
Primary Panel -2001 6 Terminals, Erie Zone Track SR601
Secondary Panel – 2001 3 terminals, Erie Zone Track SR301
4/22 Note: Five Grundfos UP15-42F zone pumps and four of the watts ¾ 200s-M5 flow check Valves were replaced.
Heating History
4/17/22
7am Zone #6 Sunroom: Thermostat manually set to call for heat. It is the only pump running. All zones were heating 25 minutes
9am Zone #1 Hot Water Maker: Runs for about 60 minutes; 2 Showers plus Laundry. Hot Water is the only pump running. All zones are heating. Temperature rises 4 degrees to 76 degrees in the entire house, outside temperature is 50 degrees.
4/18/22
Zone #6 Sun Room: Thermostat manually set to call for heat. It is the only pump running. All zones were heating in 25 minutes. Only Pump #6 is running
10/5/22
6am Zone #2 Sun Room: Thermostat manually set to call for heat. Master Bedroom: only pump running. All zones were heating in 25 minutes
10/6/22
6am Zone #6 Sun Room: Thermostat manually set to call for heat. Sunroom: only pump running. Heating Living room/Dining Room/Hall
10/21/22
9am Zone #2 Master Bedroom: Thermostat manually set to call for heat. Master Bedroom: only pump running. All zones were heating in 25 minutes. Outside temperature is 45 degrees.
12am Zone #4 Front Corner Bedroom and Rear Corner Bedroom: Thermostat manually set to call for heat. Corner Bedrooms: only pump running. All zones were heating in 25 minutes. Outside temperature was 52 degrees
When any zone calls for heat, the (one) circulator pump operates properly, however all zones make heat. Only five of the seven four watts ¾ 200s-M5 flow check valves were replaced.
Update
10/22 11:07 Oops - My son just told me he only replaced only two check valves. MY BAD.
Heating Zones
#1 Hot Water Maker 80 gallon
#2 Master Bedroom – Cast Iron Baseboard
#3 Garage – 8ft Radiator
#4 Front corner Bedroom and Rear Corner Bedroom – Cast Iron Baseboard
#5 Radiant - Kitchen and adjoining Family Room
#6a Split Zone- Sunroom –Cast Iron Baseboard
#6b Split Zone - Available (not used)
#7 Available (no pump)
#8 Living room and Dining room - Cast Iron Baseboard
Mechanical Info.
Boiler- 2001 Utica DV200B 200,000btu
Boiler Controls – Replaced in 2009. Tekmar 260
Hot Water Maker – Replaced in 2017. Amtrol Boilermate CH-80Z
Primary Panel -2001 6 Terminals, Erie Zone Track SR601
Secondary Panel – 2001 3 terminals, Erie Zone Track SR301
4/22 Note: Five Grundfos UP15-42F zone pumps and four of the watts ¾ 200s-M5 flow check Valves were replaced.
Heating History
4/17/22
7am Zone #6 Sunroom: Thermostat manually set to call for heat. It is the only pump running. All zones were heating 25 minutes
9am Zone #1 Hot Water Maker: Runs for about 60 minutes; 2 Showers plus Laundry. Hot Water is the only pump running. All zones are heating. Temperature rises 4 degrees to 76 degrees in the entire house, outside temperature is 50 degrees.
4/18/22
Zone #6 Sun Room: Thermostat manually set to call for heat. It is the only pump running. All zones were heating in 25 minutes. Only Pump #6 is running
10/5/22
6am Zone #2 Sun Room: Thermostat manually set to call for heat. Master Bedroom: only pump running. All zones were heating in 25 minutes
10/6/22
6am Zone #6 Sun Room: Thermostat manually set to call for heat. Sunroom: only pump running. Heating Living room/Dining Room/Hall
10/21/22
9am Zone #2 Master Bedroom: Thermostat manually set to call for heat. Master Bedroom: only pump running. All zones were heating in 25 minutes. Outside temperature is 45 degrees.
12am Zone #4 Front Corner Bedroom and Rear Corner Bedroom: Thermostat manually set to call for heat. Corner Bedrooms: only pump running. All zones were heating in 25 minutes. Outside temperature was 52 degrees
0
Comments
-
post a general distant picture, or 2 from a second angle, of the boiler, circ, and valves, and piping to the ceiling,
all in one shot,
someone will see somethingknown to beat dead horses0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements