Understanding Static Pressure in my heating system.
JackW
Member Posts: 236
in Gas Heating
I'm trying to understand the static pressure readings of my heating system. I've watched dozens of videos on YT, but I still can't grasp what I'm reading. It's a downflow system; there is no A-coil, and the only obstruction is the furnace filter. As you can see in the photo, I have a hole above the filter and below the furnace. I've also included a picture, a bad one, with the w/c number circled. It reads 0.70 IWC or 0.174 KPA. A one-minute reading produces a .31 max, a .19 low, and a .26 average. Are these readings telling me anything?
Thanks,
Jack
Thanks,
Jack
0
Comments
-
-
JackW said:@ChrisJ, I have one below the furnace itself. Is that not the same?
The top one is measuring suction (before the fan) and the bottom measures pressure (after the fan). The gauge adds them together.
If you move the top one to just after the filter its going to show more pressure drop, sometimes a lot more. Right now you're measuring the suction before the filter is having an effectSingle pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment1 -
The open return is perverting the TESP. Close it with tight fitting magnetic strip, sheetmetal cover or removable tape.
What is that below the furnace? Looks like an A coil to me with my weak eyes.0 -
Bob Harper said:The open return is perverting the TESP. Close it with tight fitting magnetic strip, sheetmetal cover or removable tape. What is that below the furnace? Looks like an A coil to me with my weak eyes.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0
-
@ChrisJ, so I need to drill a hole below the filter, and I don't need the probe above the filter? Do I need the probe below the fan, or do I just use one probe? What do you mean by "looking like an evap"? We don't have central A/C, so there is no A-coil.
Thanks.0 -
@Bob Harper, I don't know what you mean by "open return." We don't have central air, so they took the A-coil out when we replaced the old furnace a couple of years ago. Thanks for your help.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements