Hy vent installed in tee on return?
99JT
Member Posts: 1
in Gas Heating
I'm in the process of installing a hydronic unit heater in my garage which is being supplied by the boiler in my house which has a taco air separator.
Question is would their be any benefit to adding a tee with a hy vent in the return line which is by far the highest point in the system
Question is would their be any benefit to adding a tee with a hy vent in the return line which is by far the highest point in the system
0
Comments
-
-
On the unit heater, should be a supply and return connection. Whichever is the highest one. If connections are at the same level on the unit, either will work
As long as you have 5 psi or more at that vent, you should not pull air in.
Assuming near boiler piping is correct, pumping away from the expansion tank
A manual vent would work, you should only need to purge it once on start up if you have a good air purger, shown by Steve, at the boilerBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 919 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements