Hy vent installed in tee on return?
99JT
99JT Member Posts: 1
I'm in the process of installing a hydronic unit heater in my garage which is being supplied by the boiler in my house which has a taco air separator.
Question is would their be any benefit to adding a tee with a hy vent in the return line which is by far the highest point in the system
  • STEVEusaPA
    Might be the highest part of the system, but on the return, probably suck in air. If you have a micro absorber air elimination anywhere on that loop, pumping away, it will take care of any air problem after initial purging.
    hot_rod Member Posts: 27,845
    On the unit heater, should be a supply and return connection. Whichever is the highest one. If connections are at the same level on the unit, either will work
    As long as you have 5 psi or more at that vent, you should not pull air in.
    Assuming near boiler piping is correct, pumping away from the expansion tank
    A manual vent would work, you should only need to purge it once on start up if you have a good air purger, shown by Steve, at the boiler