Zoning and venting question
acura22itr
Member Posts: 11
in Gas Heating
Hey guys .. I’m installing a 3 zoning valves … do i need to have “auto vent “ on each zoning valve ? See pic
0
Comments
-
No. A single scoop or air eliminator on the supply side before the circulator will suffice.0
-
Thank you @DJD7750