Zone Valve Taco Powerhead
heatingdude
Member Posts: 9
in Gas Heating
Hi guys,
I have a boiler with three zones therefore three thermostats. One of the thermostats is a nest and reads there’s no power to Rh. I took of the thermostat and tested Rh to W and got 0 volts so I went down to the zone valve. I tested from terminal two to ground and got 0V while the other zone valves read 24V to ground. I decided to just turn on the other two to make sure they work and they kicked in. However they took a while to kick in and when I took off the thermostat (to the ones that were working) and tested Rh to W I got 0V which confused me. Is it possible that all three zone valves are going bad?
I have a boiler with three zones therefore three thermostats. One of the thermostats is a nest and reads there’s no power to Rh. I took of the thermostat and tested Rh to W and got 0 volts so I went down to the zone valve. I tested from terminal two to ground and got 0V while the other zone valves read 24V to ground. I decided to just turn on the other two to make sure they work and they kicked in. However they took a while to kick in and when I took off the thermostat (to the ones that were working) and tested Rh to W I got 0V which confused me. Is it possible that all three zone valves are going bad?
Attached below is the wiring diagram
if someone could help it would be much appreciated.
if someone could help it would be much appreciated.
0
Comments
-
The zone valves that worked are ok. The valve actuators have a wax element that takes 60-90 sesonds to heat up and work.
You won't get voltage between R & W in most cases the thermostat is just a switch.
A nest thermostat will not work dependably without a "C" or common wire. Your going to need some rewiring and a 3 wire cable to the Nest to make it work1 -
how about that maybe you wired it wrong. thermostat transformer should be wired 1-2. system transformer should be 2-3. common tap is #2. move blue to #20
-
EBEBRATT-Ed said:The zone valves that worked are ok. The valve actuators have a wax element that takes 60-90 sesonds to heat up and work. You won't get voltage between R & W in most cases the thermostat is just a switch. A nest thermostat will not work dependably without a "C" or common wire. Your going to need some rewiring and a 3 wire cable to the Nest to make it work0
-
pedmec said:how about that maybe you wired it wrong. thermostat transformer should be wired 1-2. system transformer should be 2-3. common tap is #2. move blue to #20
-
Hello @heatingdude,
Did you start at the secondary of the transformer (Brown and Pink) and verify your meter works correctly and you have it set to a AC (Alternating Current) Voltage range above 24 VAC. If it is set on DC (Direct Current) it may read zero Volts.
Also I agree with @pedmec the wiring looks odd, maybe 1 and 2 on the Zone Valve are reversed on the drawing.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
109A_5 said:Hello @heatingdude, Did you start at the secondary of the transformer (Brown and Pink) and verify your meter works correctly and you have it set to a AC (Alternating Current) Voltage range above 24 VAC. If it is set on DC (Direct Current) it may read zero Volts. Also I agree with @pedmec the wiring looks odd, maybe 1 and 2 on the Zone Valve are reversed on the drawing.0
-
Hello @heatingdude,
Obviously the transformer is probably good, since the system mostly works. What you wrote is your meter reads zero with every measurement you made.
The meter at the transformer is to VERIFY THE METER AC Volts operation, not the transformer and not to measure DC. Your wiring diagram is not typical, however if it is factual it may work with your boiler.
If you are using defective test equipment or test equipment set up wrong you will be confused.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
powerhead takes roughly two minutes to open and for the end switch (2-3) to make which initiate call for the boiler to come on.
you should have two transformers in this system although after looking at the drawing it looks like they are using the (1) system transformer to power the boiler and powerheads. Because of the way its wired you won't read 24 volts if the heater switch, which is located in the powerhead, is failed in the open position. measure from 1 and 2 at the zone valve with the thermostat closed and you should get 24 volts.0 -
If you have voltage at the powerhead as described then your powerhead is defective.0
-
pedmec said:If you have voltage at the powerhead as described then your powerhead is
defective.0 -
Hello @heatingdude,
Keep in mind there is a switch to keep the Wax Motor from overheating. See red circle in picture. This switch may make the NEST unhappy and give you unexpected voltage readings depending on the state of the Zone Valve.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
109A_5 said:Hello @heatingdude, Keep in mind there is a switch to keep the Wax Motor from overheating. See red circle in picture. This switch may make the NEST unhappy and give you unexpected voltage readings depending on the state of the Zone Valve.0
-
Hello @heatingdude,
Sounds like the expensive way to maybe fix it. As others stated I probably just needs a C wire to make the NEST happy.
Red oval in pic shows the switch.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
The first thing that you need to determine is whether you have two wires at the old thermostat or three or more wires in the cable from the new Nest thermo to the zone valve.
The two transformers in 109A-5's diagram is the power transformer to the Nest and the other transformer is in the aquastat on the boiler.
0 -
109A_5 said:Hello @heatingdude, Sounds like the expensive way to maybe fix it. As others stated I probably just needs a C wire to make the NEST happy. Red oval in pic shows the switch.0
-
Regardless of whether you have a c wire if you measure between r and w at the thermostat and you have no voltage then you have a break in the path of circuitry. Because of how it is wired the only other controlled break is at the heater, as 109a_s has circled in the drawing.0
-
pedmec said:Regardless of whether you have a c wire if you measure between r and w at the thermostat and you have no voltage then you have a break in the path of circuitry. Because of how it is wired the only other controlled break is at the heater, as 109a_s has circled in the drawing.0
-
Hello @heatingdude,
OK, you are going to replace the NEST with an inexpensive Non-NEST thermostat. That makes sense to me. When you said "change the thermostat" I thought you meant with another NEST.National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Looks like you have a lot of help with wiring nest thermostat. It does take 1.5 min to open ZV, and make endswitch close to fire boiler.If you continue to have problems.Call Taco tech support at 401-942-8000 and ask for tech support.
they can walk you through it.Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0 -
@heatingdude Please see the wiring diagram attached page 6, showing how to wire in a 570 series heat motor zone valve to your Nest. As Joe Mat suggested you can always call into Taco Technical Services during normal business hours 8am-5pm est. Mon-Fri and just ask for Technical Services.0
-
SteveSan said:@heatingdude Please see the wiring diagram attached page 6, showing how to wire in a 570 series heat motor zone valve to your Nest. As Joe Mat suggested you can always call into Taco Technical Services during normal business hours 8am-5pm est. Mon-Fri and just ask for Technical Services.1
-
Hello @heatingdude,
Keep in mind the TACO diagram assumes two transformers, one shown in the diagram and one internal to the boiler to power the boiler's equipment when the TT is closed (Zone Valve End Switch closure). And that method is what most are probably used to seeing.
I suspect your system only has one transformer and that is the reason it is wired the way it was.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Sorry I did not see this until today. There is a very simple solution. When wiring a 2 wire thermstat to a taco zone valve there is no problem wiring thermostat W to #2 and transformer C to number 1. and the punk wire on the transformer to the R on the thermostat. that is because W and R on the thermostat could also be labeled T and T. There is not difference between the ends of a switch. Electric is colorblind and cant read.
Both diagrams will work with only 2 wires
When you introduce a thermostat that requires a C to operate then T T no longer applies. that is because one of the T terminals must be R and the other T terminal is then the W on the thermostat. The wire that becomes R on the thermostat must be powered from the R on the transformer. The W on the thermostat then must go to #1 on the zone valve (Not 2 as shown). On your Control system the R must be the Brown wire on the transformer. That makes the C on your control system transformer the pink wire. That is attached to the Red wire and attached to the Blue wire in your diagram. Since the C wire (Pink) from the transformer must be connected to the common wire of the zone valve (that is the #2 post on the zone valve) and needs to be connected to the C on the thermostat, then the only option for the W on the thermostat must be connected W to #1 on the zone valve.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Try this
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements