Fan limit switch on old furnace.
Tonylc4
Member Posts: 2
in Gas Heating
I have an old furnace, any one have an idea what type of fan switch I can replace this one with. 
Problem is the fan switch won’t come up unless I put in Manual then back to auto.


0
Comments
-
for starters look at the max temp on the ratings plate on the furnace and set the limit stop to that, then try moving the on stop up a bit and the off stop down a bit. if you have to replace it, you can get a combination fan/limit control from honeywell/resideo or white rodgers or robertshaw. you will need to pull it out and measure the probe length. The modern resideo control has a white knob for the manual control instead of that rocker. They are available from supplyhouse.com.1
-
-
Thank you! Ch4man0